I was called out to a fault today where the newly fitted consumer units RCD was tripping when the cooker was switched on.The cooker had been checked by an appliance engineer and deemed to be fully working with no faults.
So I turned up to be presented with a nice new shiny MK metal clad dual RCD board.Upon removing the lid I was presented with this
20180814_132909.jpg


Also notice the top of the board as below....



20180814_132900.jpg


Upon asking about the board change the customer said that they had bought the board and a nice young guy had fitted it for £100!
The board was not labeled what so ever with grommets missing etc.
No paperwork had been supplied and no testing done.

The fault on the cooker was found to be the neutral put in the opposite bar to the one it should have been in.This was quickly rectified but i started to write a list of what was wrong(I am sure there are even more than this)

1.Mains tails not double covered 25mm.
2.Main earth was only 6mm feeding the unit.
3.No grommets or bushes in any holes.
4.Huge hole where tails entered unit (easily stick a finger in there) and no bushed glands for tails.
5.Green/yellow sleeving missing off a lot of earth wires.
6.No mains gas or water bonding.
7.Unit not marked up and no warning labels anywhere.
8.No test certs or Part P supplied.
9.Consumer unit only fixed with 2 screws at the top and none at the bottom so the board was flapping.
10.Old rubber cable still connected(showing a very low neutral to earth fault.
11.A twin and earth with just its earth and neutral connected but not the live with very low tests showing.
12.Mains tails sticking out of main switch with copper showing.
20180814_140225.jpg


13.Four 2.5mm cables in one breaker.
14.40 amp breaker feeding cooker circuit.(I would have put it on a 32amp)
15.Muliple lighting cables in one breaker.
I am sure there are many more faults that I haven't been bothered to find so feel free to chip in.:p

The customer said "Should I call him back to put it right?"
I said you should only call him back to give him a slap :fearscream:and would not want this guy touching any electric ever again.
I have given the customer a quote to redo the consumer unit again with bonding,testing,certification etc but by the way he was talking about getting the young lad back then I doubt I will be doing anymore work.:angry:
 
The customer said "Should I call him back to put it right?"
I said you should only call him back to give him a slap :fearscream:and would not want this guy touching any electric ever again.
I have given the customer a quote to redo the consumer unit again
considering he put it in then a EICR is in order not a EIC.
your customer needs to speak to local b/c. before work is carried out .
 
if i had an asset worth 100 grand+ i wouldnt skimp on maintenance, what happens if the house burns down and it turns out the insurance wont cover you because you had a plumber fit a distribution board?

its like the diyer who takes down a light fitting, is confronted with permanent live at fitting, takes it all apart and then tries to put it back together without the faintest idea of what cable does what! and after having made a 2 minute job a 30 minute job calls in an electrician to get the job done for the same price as it would have been to begin with!
 
if i had an asset worth 100 grand+ i wouldnt skimp on maintenance, what happens if the house burns down and it turns out the insurance wont cover you because you had a plumber fit a distribution board?

its like the diyer who takes down a light fitting, is confronted with permanent live at fitting, takes it all apart and then tries to put it back together without the faintest idea of what cable does what! and after having made a 2 minute job a 30 minute job calls in an electrician to get the job done for the same price as it would have been to begin with!
I generally charge more to fix the lighting ****ups after they have made a mess of it after having a go themselves. It generally takes longer as well, so a justifiable charge.

Have had a few where, for some reason only know to them they have connected the looped live to the earth of the metal light fitting.
 
I often don't, if the existing 16mm tails are of sufficient length and in good order and the DNO fuse is 60 or even 80 amps I don't see the need. How many domestic installs actually need 25mm tails - especially when the incoming supply is 16mm ?! And 25mm can be a right pain to work with when space is tight....
i swap like for like, old tatty red/black meter tails look grubby on a new board, pop those old tails in the scrap bag
 
I thought the whole purpose of Part P being introduced was ostensibly to put an end to these rogue installs and raise industry standards?

Yeah it was I think but its only notifiable work really so any one can change a light in the living room or so. also how can part p be enforced on a diyer who's working on there own home it can't really unless someone gets hurt from it I suppose then they can but then its already too late
 
Good video, JK! Clearly illustrates the best way to assess the length of earth sleeving to cut for a particular CPC! I mean, how else would you do that???

Static Zap, a bampot is a fully qualified, all-round, certified and experienced eejit!

An eejit is a fully qualified, all-round, certified...


bampot!

Simple, really!
 

Reply to Where do these cowboys come from? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top