Discuss Which certificate for a new CCU? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
9
I'm newly registered and still gaining experience. Have successfully posted on here recently.

A client has asked me to fit a new consumer unit for them. I presumed I would also need to do a full visual inspection including testing (within limitations) of their existing circuits.

I am unsure which certificate goes with this? Would it be an Installation or Condition or Periodic?

Thanks in advance

Chris
 
Source: http://www.electricalsafetyfirst.org.uk/mediafile/100126672/Best-Practice-Guide-6.pdf

10.1 States: The alteration or addition itself (the installation of the replacement consumer unit and any other new work, such as additional final circuits) should be verified fully in accordance with the requirements of Section 610 of BS 7671 (as amended) and an Electrical Installation Certificate in accordance with BS 7671, detailing the work, should be given by the installer to the customer.

If you read on....
10.4. If a full Electrical Installation Condition Report on the installation has not been provided as part of the work, consideration should be given by the installer to stating this on the certificate with a recommendation this should be done.

Before you change the CCU, you are supposed to do an EICR or if the customer refuses you to do this, a pre-work survey.

Section 7.2 (Planned change) Of the document goes into more detail on this.
 
Last edited:
Issue a EIC, but before you start you must find out the state of existing wiring. As when you introduce RCD you may find it wont stay on as the existing wiring is shot. As the above post alludes to, go read the best practice guide on Electrical Safety First website. A lot of guides and useful info there from a credible body.
 
I'm newly registered and still gaining experience. Have successfully posted on here recently.

A client has asked me to fit a new consumer unit for them. I presumed I would also need to do a full visual inspection including testing (within limitations) of their existing circuits.

I am unsure which certificate goes with this? Would it be an Installation or Condition or Periodic?

Thanks in advance

Chris

Try a little logical thought before asking questions.
You need to certify your work, so it must be a certificate and therefore you couldn't use an eicr because that is a report. there will be multiple circuits therefore a minor works is unsuitable, which leaves the eic as the only possible option.
Also you don't have the option to apply limitations to the testing for an eic, that is only for a periodic inspection and test for producing a report. The testing you will do I shall to prove that the installation is safe to be energised and then handed over to the customer.
 

Reply to Which certificate for a new CCU? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
Hi there. I’m hoping for some advice. I currently run a small limited company that provides IT services, both commercial and domestic so I...
Replies
0
Views
625
Hi Everyone, I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back...
Replies
28
Views
3K
Hi wondering if you could help with some advice Been running an Essex/suffolk based electrical firm for last 20 years, mainly light commercial...
Replies
1
Views
549
Good morning, I'm in the process of a partial refurbishment which will involve the present kitchen being changed into a bedroom instead and the...
Replies
3
Views
872

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock