  1. Aaron Roberts
    Offline

    Aaron Roberts Guest

    I'm changing my old rewirable cu for a new dual rcd board and must also replace the old isolator located away from the cu. It's next to the meter which is over 3 metres away in the front porch.

    Which type of isolator should I use and how should it be fitted e.g. in an ip rated enclosure using blind grommets with slits in. Is this method in breach of the regs ip4x?

    Please help :)
     
  2. thw1965
    Offline

    thw1965 Guest

    well if its in a covered waterproof porch it wont require a waterproof enclosure. Any double pole isolator with the appropriate ampage rating, they are normally 80 or100 amps will do.
     
  3. Knobhead
    Offline

    Knobhead Guest

    HaHa now go walking the trolls
     
  4. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    It will need to be an over current protective device, not isolator. As you are 'fusing down' to protect the tails.
    I'd suggest a switched fuse unit
     
  5. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    Also IP4X is only for a readily accessible top surface, The rest you need to achieve IP2X.
    And additional protection for tails if buried in a wall, by rcd or other means.
    Hope this helps
     
  6. WPD Lad
    Offline

    WPD Lad Guest

    Sounds like you'll need a KMF depending on the route of the tails
     
  7. High Tower
    Offline

    High Tower Trusted Advisor

    Location:
    Birmingham
    kmf or if your feeling flush, a wylex 110/M switch fuse
     
  8. Engineer54
    Offline

    Engineer54 Guest

    An isolator won't cut it i'm afraid, it needs to be an appropriately rated switch fuse.
     
    • Like Like x 1
  9. Richard
    Offline

    Richard Electrician's Arms

    Always used a KMF in this situation. Rich
     
  10. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    firstly ...you need to be sure that the new position for the C/U is OK.....that is to say that the C/U and anything alse asocciated with this install (earthing....bonding ...both main and supplementary) etc is up to the latest edition of BS7671...before undertaking ANY WORK HERE...............
     
  11. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    and to make sure that theres no external influeses (mutual detrimental influenses)such as hot pipework.....band 2`s..or any other sillyness like that................
     
Loading...
Similar Threads - type isolator tails Forum Date
Mitsubishi MCCB F-type and V-Type Operating Handles Industrial Electrician Talk Jan 24, 2018
Type of cable...looks like fp200 New Member Introductions Jan 22, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job