    Can anyone help me please?

    I'm looking to install a whirlpool bath pump in a domestic bathroom.

    The instructions say I have to wire the system independently, but I was hoping to spur off the domestic socket circuit in an adjoining bedroom too a fused switch outside the bathroom. Is this OK? The consumer unit is at the other side of the house!

    I've searched these threads, and the only reference I can see condoning using a separate supply refers to the possibility that the motor might cause nuisance tripping? In that case should I use a second RCCB in-line with the fused switch?

    I'd be obliged for any clarification.
     
  2. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    Are you a sparky?

    IMHO the manufacturers instructions should be complied with.
     
  3. Duncan Bennett
    Offline

    Duncan Bennett Electrician's Arms

    In another life, Murdoch. I got my sjib grade card back in '79 but gave up the tools about 12 years back when my life took another direction. I'm currently in the process of registering for BS7671 and ECS H&S Assessment.

    In re-reading the instructions it says " ... must be wired independently. Do not use the same power supply as other appliances" Which I read as, don't loop the supply from a towel-rail, heater, shower, etc.

    I fully intend complying with the manufacturers instructions, i'm just not sure if i'm interpreting them correctly and wondered if someone could help me clarify.
     
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    instructions a bit ambiguous. i suppose if you wire a FCU off the RFC, that's independent. that's how i would do it. 3A FCU .
     
  5. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    In which case what is the specified load of the device?
     
  6. Duncan Bennett
    Offline

    Duncan Bennett Electrician's Arms

    Cheers, Guys.

    There is a 1100w water pump, and a 350w airblower - both at 240v

    Is a combined RCD/FCU such as the Volex 13A RCD FCU an option?

    Again, really appreciate your help :)
     
  7. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    oops, a bit over my 3A. the only problem you'll have with a RCD FCU is no discrimination with the existing RCD in the CU ( assuming that the RFC is on RCD)
     
  8. Murdoch
    Online

    Murdoch Electrician's Arms

    Location:
    Woking
    As Tele says, but would suggest a 10A fuse in the FCU. I'm guessing you've checked the bonding?? and this is notifiable too!
     
    Last edited: Feb 22, 2012
  9. Duncan Bennett
    Offline

    Duncan Bennett Electrician's Arms

    Thanks again. Is there any reason why the pump's should cause nuisance tripping. Isn't it much the same scenario with a dishwasher motor, or washing machine - even a vacuum cleaner?
     
  10. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    use a double pole FCU, then it can be isolated. should not cause nuisance tripping unless faulty. might have some leakage ( of water) if a plumber has fitted the thing.
     
    • Like Like x 1
  11. Duncan Bennett
    Offline

    Duncan Bennett Electrician's Arms

    To be honest, I only got a quick sneak peak this afternoon. The original bath has been taken away and the new whirlpool bath is in situ but not fixed down or plumbed in yet. In my days we ran a separate 6mm earth to the bathroom and kitchen, so I'm assuming that is there and I just didn't notice it. The house itself is only about 10 years old.
     
  12. Dannyspark
    Offline

    Dannyspark Active EF Member

    Location:
    Wiltshire
    He's not talking about that bonding, he's on about the equipotential bonding of the gas/water supplies.

    If the CU has a 30ma RCD and the gas/water supplies are bonded back to the CU in 10mm cable (if it's a TNCS suply) then all you need do is add an FCU to the nearest ring outside of the bathroom and fuse it down to whatever your load works out to.........simples!

    If there isn't an RCD in the CU then you can add a combined RCD/FCU as you already suggested instead of the standard FCU. You still need to check the bonding though.
     
  13. Duncan Bennett
    Offline

    Duncan Bennett Electrician's Arms

    Thanks guys. Much appreciated :))
     