Discuss why is volt drop important??? in the Australia area at ElectriciansForums.net

B

bobbybrown

whats the reason we worry about volt drop?
It cant be because of the design of fittings etc.. because the actual voltage can be 230v +10% -6% percent,
i believe if there is a voltdrop then the current will increase as per ohms law
maybe its something to do with potential differences e.g 230 at one end and 236.9 at the other (3%) however i dont understand why would that cause concern????
 
so as current increases the cable would in as simple a term possible get hotter and probably beyond its specs. Sure someone else will explain it in a lot more depth. btw the current should not increase just because the voltage drops. I think im right
 
Last edited by a moderator:
try running fluorescent lighting at 205v. it flickers more than a 1920's movie.
 
The current will not increase because the resistance of the circuit stays the same, so the current will reduce.

The reason is as eluded to in the op, for the satisfactory operation of any connected equipment.
 
whats the reason we worry about volt drop?
It cant be because of the design of fittings etc.. because the actual voltage can be 230v +10% -6% percent,
i believe if there is a voltdrop then the current will increase as per ohms law
maybe its something to do with potential differences e.g 230 at one end and 236.9 at the other (3%) however i dont understand why would that cause concern????


Not true - are you thinking of transformers?

If you reduce the voltage you will reduce the current and so reduce the power:)


edit - great minds andyb ;)
 
Last edited by a moderator:
"So you want it to trip all the time ? i think not so in your design you allow for voltage drop, your allowed 5%"
errrr you lost me why would it trip all the time??

just want to know why its 3% on lighting and 5% on other, and why this would matter if the nominal voltage is 230 +10 - 6???
 
Operating electrical equipment below its acceptable voltage rating can lead to premature failure and hazardous situations.
Inductive loads, such as motors and ballasts can overheat, shortening equipment life and increasing energy consumption.
If operated below their rated voltage, resistive loads, such as heaters, simply won't provide the desired output.
A 10% reduction of voltage reduces the power output by 19%, because power output reduces as the square of voltage.
Reduced circuit voltage can cause lights to flicker when other appliances or equipment cycle on.
 
"So you want it to trip all the time ? i think not so in your design you allow for voltage drop, your allowed 5%"
errrr you lost me why would it trip all the time??

just want to know why its 3% on lighting and 5% on other, and why this would matter if the nominal voltage is 230 +10 - 6???

because some lighting is very sensitive to reduced voltage. The 230 +10 -6 figures are only what the DNOs guarantee lose more than 3% on 224V and fluorescent lighting is going to really struggle.

EDIT : and for a really good answer read the one above!
 
Last edited by a moderator:
just another quick question regrading volt drop, the 3 percent rule on lighting, is that 3 percent on the actual measured voltage or 3 percent on 230v?

imo it would make sense to be based on 230v and not measured voltage . e.g if your supply was 1 percent over 230v then you should be allowed up to 4 percent volt drop

i know the further you are away from the substation the lower your measured voltage will be, out of interest does it drop much or will it still be nearly at 230v?
 
just another quick question regrading volt drop, the 3 percent rule on lighting, is that 3 percent on the actual measured voltage or 3 percent on 230v?

imo it would make sense to be based on 230v and not measured voltage . e.g if your supply was 1 percent over 230v then you should be allowed up to 4 percent volt drop

i know the further you are away from the substation the lower your measured voltage will be, out of interest does it drop much or will it still be nearly at 230v?



the 3% figure is on 230 V as that is what you should expect even though reality is that it will often be more. So for lighting you calculate for Vd to not exceed 6.9volts :)

edit: in my experience supply voltage has always exceeded 230V
 
Last edited by a moderator:

Reply to why is volt drop important??? in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
hi This is just a starter because I haven't done any measurements yet (I was a guest there) and what I can do will be restricted as this has never...
Replies
10
Views
3K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
Hi folks I am retired and only tend to read the weekly summaries. I read the long-winded thread re. the storage heater and MCB tripping (thread...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock