Hello Peeps,
Advice please.
A customer has a 10kw wind turbine, this is configured as split phase.

He's had to install 3 phase but the company that put the turbine in only installed a 3 core swa to the turbine, whoops.
This normally would be ok but the control gear requires a neutral.
The plan was to install a single core swa and put it in the same trench as the existing swa.
Spoke with the niceic and they say its a complete no.
Can any of you guys see why this is this case?
regards
Paul
ps hope i have made sense.
 
Hello Peeps,
Advice please.
A customer has a 10kw wind turbine, this is configured as split phase.

He's had to install 3 phase but the company that put the turbine in only installed a 3 core swa to the turbine, whoops.
This normally would be ok but the control gear requires a neutral.
The plan was to install a single core swa and put it in the same trench as the existing swa.
Spoke with the niceic and they say its a complete no.
Can any of you guys see why this is this case?
regards
Paul
ps hope i have made sense.
What reason did the NICEIC give? if it was up to me I would get the dipsticks who installed the turbine and the cable back to do it right at their expense, or was a 3 core specified at the outset.
 
to be truthful i am not sure who specified 3 core?
The niceic have quoted parallel conductors from the regs but i cant see anything in there about this.. My mate has been dealing with them and i haven't spoke with him propley about this, just got a text off him.
I personally cant see a problem so long as there in the same trench.
All hv cables are singles.
 
to be truthful i am not sure who specified 3 core?
The niceic have quoted parallel conductors from the regs but i cant see anything in there about this.. My mate has been dealing with them and i haven't spoke with him propley about this, just got a text off him.
I personally cant see a problem so long as there in the same trench.
All hv cables are singles.
No they aren't
 
Maybe they are using 521.8
Each part of a circuit shall be arranged such that the conductors are not distributed over different multi core cables

What about installing a isolating transformer and make your own neutral
 

Reply to Wind turbine in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
642
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hello, I'm not an electrician. I'm looking for advice on the capacity of an existing SWA cable I have on a farm. It's a three phase cable...
Replies
5
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hello everyone my name is Tarek, i work as a concert and show lighting operator with over 20 years of experience in this field, so i have gained...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock