You don't necessarily need to provide a separate OCPD for each appliance as long as fault protection is OK for the tail to each appliance. Also check manufacturers instructions in case they specify a fuse size,which regardless of how pointless it seems you will have to comply with. Otherwise I would just link the incoming 6,0mm(?) between 3x 20a DP isolators,MK (for example) 20a isolators will take 2x 6.0mm conductors, because I have terminated them in the past. Or you could use 32a isolators if you prefer. 45mm deep back boxes will be a good idea, 35 will be tight....don't even think about 25mm
 

Reply to Wiring 3no 3.2kw 16amp ovens to an existing 32amp 6mm supply in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock