Discuss Wiring a Hive receiver to a Vokera Linea Combi boiler in the Central Heating Systems area at ElectriciansForums.net

Rupe

-
Reaction score
0
Can anyone please help me to wire a Hive to a Vokera Linea Combi Boiler

I have uploaded diagrams and pictures of everything I think is important. I think I should

1 Disconnect the Honeywell thermostat and bridge the two connectors where it says Room Thermostat on the wiring diagram.

2 Disconnect the 4 wires to the programmable timer on the boiler ( see Vokera wiring diagram)

3 connect L on the boiler to L on the Hive

4 connect N on the boiler to N on the Hive

5 connect a wire from the lower of the two TA on the boiler ( see Vokera wiring diagram) to the ‘heating on’ on the Hive

6 connect a wire from the connector with an equals sign just above the higher TA to the ‘Common’ on the Hive (see Vokera wiring diagram)

7 connect an earth from boiler to Hive

Is my thinking correct? Any help would be much appreciated.

Rupe

0A0B4E45-E20C-43D5-8735-8003276186C1.jpeg

72B823AB-0991-403D-9BC0-DD8EC3CCE17A.jpeg

9DC98AE4-5226-4F87-B438-443B97F686FF.jpeg

A136DFC9-9EE3-4E41-BF1B-D7FBA205510D.jpeg

939FCF35-4082-40EB-88CE-761486932192.jpeg
 
You've already answered your own question. The Brown and blue are the switch wires that you need. The Hive receiver needs its own LNE ( hive is class2 anyway) put the receiver next to the boiler, cut stat wire back and wire brown into (1) and Blue into (sleeve with marker) (3)..job done. you'll need to tell the programmer to have heating on constant and Hive will do the switching. any q's PM me.
 
You've already answered your own question. The Brown and blue are the switch wires that you need. The Hive receiver needs its own LNE ( hive is class2 anyway) put the receiver next to the boiler, cut stat wire back and wire brown into (1) and Blue into (sleeve with marker) (3)..job done. you'll need to tell the programmer to have heating on constant and Hive will do the switching. any q's PM me
FFS WE NOT ALLOWED TO GIVE OUT HOW TO DO IT .
 
You've already answered your own question. The Brown and blue are the switch wires that you need. The Hive receiver needs its own LNE ( hive is class2 anyway) put the receiver next to the boiler, cut stat wire back and wire brown into (1) and Blue into (sleeve with marker) (3)..job done. you'll need to tell the programmer to have heating on constant and Hive will do the switching. any q's PM me.
Many thanks Frank. I will give it a go.
Rupe
 
You've already answered your own question. The Brown and blue are the switch wires that you need. The Hive receiver needs its own LNE ( hive is class2 anyway) put the receiver next to the boiler, cut stat wire back and wire brown into (1) and Blue into (sleeve with marker) (3)..job done. you'll need to tell the programmer to have heating on constant and Hive will do the switching. any q's PM me.
Hi Frank, just wanted to thank you for your help with my wiring. It’s all working great now! All the best. Rupert
 

Reply to Wiring a Hive receiver to a Vokera Linea Combi boiler in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Hi. As per header. I just want to make sure I do this correctly. Remove old wires from X9 7 and 8 and link these two (from another thread on...
Replies
0
Views
553
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
500
hi need help with wiring this. basically new build with combi boiler, unvented cylinder with dual channel hive ive attached pics with the wiring...
Replies
39
Views
6K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Hi Guys, i have a gledhill boiler mate 2000, how do i change the programmer so its connected to the hive L N 3? i have tried just changing the...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock