Mikeymike77

Hey I am trying to do this formula but I can't work out the last number to get answer the bit I can't do is the 10-6 to get the answer.


frequency of 1 KHZ


2x3.142x1000 x220x10-6 - = 723.4ohms

Frequency 20 KHZ

2x3.142x20000x220x10-9 = 36.2ohms

Can anyone describe how to do the last number? Because on a calculater I don't the same number in ohms ?
 
Last edited by a moderator:
Where to start?

What is this, a given answer or fruit of your efforts?

The top calc is correct - but only if you square (you`ve written "x2" :eek:)

The 3.142 gave it away, as in, you`d use Pi x r to the power of 2 (squared) but instead you`re using a Hz value.

Also, you`d need to substitute 230 instead of your 220 - i guessed this was Voltage (again you kept us in the dark :mad:)

The `bit` you say you`re stuck on - the `to the power of -6` part was the easy bit :D

x10 -6 is 1 micro units (whatever you`re working in) In other words it`s 10 /10 with 6 zero`s after it (10,000,000) The minus symbol indicates you must invert the x into divide.

Therefore in the 2nd calc, the x10 -9 will be in nano units (10 /10,000,000,000) Just basic scientific notation

Unfortunately, knowing that doesn`t really help tho` as the 2nd calc is screwed up somehow - have you an idea i wonder? :confused: Let us know if you figure out where.

Hope this helps
 
Last edited by a moderator:
Hi.

I been looking at your calcs for a while now and I think theres deffo something wrong with calc 2 somewhere.

I cant put my finger on it just yet as I dont have all the info i.e the original calc/question.

Anything with a - in fornt must be divided to gain the base unit unit i.e 10-6 would be 10,000,000 as a base unit - a micro unit.

Cheers.


ElectricAl beat me to it.:p
 
Last edited by a moderator:
The first one is an inductance ie 2times pie, times frequency, times inductor. The second is capacitance, and the answer should be, one over, 2 times pie, times frequency, times capacitor. This gives 36.172 ohms which is near enough for anybody.
 
Last edited:
I thought when working out impediance you needed first to work out both Inductive Resistance and then Capacitive resistance.

Inductive Resistance is:

XL = 2*pi*f*L

Where f is Frequency (Hz) and L is Inductance (H)

Capacitive Resistance is:

XC =

1
-------------
2*pi*f*C

Where f is Frequency and C is capacitance (farads)



You then need the formular : Z = Sqrt R2 + (XL - XC)2

Is this correct?
 
Last edited by a moderator:
Hey I am trying to do this formula but I can't work out the last number to get answer the bit I can't do is the 10-6 to get the answer.


frequency of 1 KHZ


2x3.142x1000 x220x10-6 - = 723.4ohms

Frequency 20 KHZ

2x3.142x20000x220x10-9 = 36.2ohms

Can anyone describe how to do the last number? Because on a calculater I don't the same number in ohms ?

it is

Capacitive Resistance is:

XC =

1
-------------
2*pi*f*C

Where f is Frequency and C is capacitance (farads)

And your answer to question 1 is incorrect decimal in wrong place, Answer = 0.7234 (I bet if you look at calculator 723.4 has a 10-4 to top right of answer.

Question 2. answer correct this is how I got it 100,000,000 / (2 x 3.142 x 20000 x 220) = 36.1715 ohms

The 100,000,000 represent convertion of 1/10-9
 
it is

Capacitive Resistance is:

XC =

1
-------------
2*pi*f*C

Where f is Frequency and C is capacitance (farads)

And your answer to question 1 is incorrect decimal in wrong place, Answer = 0.7234 (I bet if you look at calculator 723.4 has a 10-4 to top right of answer.

Question 2. answer correct this is how I got it 100,000,000 / (2 x 3.142 x 20000 x 220) = 36.1715 ohms

The 100,000,000 represent convertion of 1/10-9

That is one way of doing it but very easy to make a mistake. You really need a calculator with an exponent key (ie. exp, ee) depending on your make and model.
 
The first one is an inductance ie 2times pie, times frequency, times inductor. The second is capacitance, and the answer should be, one over, 2 times pie, times frequency, times capacitor. This gives 36.172 ohms which is near enough for anybody.

mike I think they are both calculation to find different Xc, if you do Xl for first question ans= 1.3824 ohms

Did not have calculator available, so i did it long hand.
 

Reply to Working out Impediance need help! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
389
Hello I've been away from the industry for awhile and I've recently got back in to it again. I never finished off all my grades. I got both my...
Replies
0
Views
679
Hi guys, I could use your expertise. I have an old automatic pool cover, kept in storage for 30+ years, in good condition, and worked well last...
Replies
0
Views
791
Hi all. In a bit of a situation which is starting to cause a fair bit of stress and figured maybe asking some silly questions here may help to...
Replies
7
Views
1K
Been asked to price for a job, customer is having attic done out so needs a few new circuits up there. Some more context I'm based in South Wales...
Replies
78
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock