Just wanted to get some opinions on the following...

Working in a bathroom conversion requiring supply for a shower pump, changing lights to downlight and power to a demister mirror.

House currently has an old CCU with wired fuses and no RCD's. And lighting circuit has no cpc.

For shower pump supply I thought using a SFCU with RCD.

For downlight with no cpc I presume I need to put N/A on cert for R1+R2 and Zs readings and add an advisory about upgrading wiring.

As for demister mirror, to be safe I was thinking of using a SFCU with RCD also.

Client assures me they are going to have a rewire but I want to make sure all my work is safe and up to regs without presuming a future upgrade to CCU.

Any thoughts?
 
Just wanted to get some opinions on the following...

Working in a bathroom conversion requiring supply for a shower pump, changing lights to downlight and power to a demister mirror.

House currently has an old CCU with wired fuses and no RCD's. And lighting circuit has no cpc.

For shower pump supply I thought using a SFCU with RCD.

For downlight with no cpc I presume I need to put N/A on cert for R1+R2 and Zs readings and add an advisory about upgrading wiring.

As for demister mirror, to be safe I was thinking of using a SFCU with RCD also.

Client assures me they are going to have a rewire but I want to make sure all my work is safe and up to regs without presuming a future upgrade to CCU.

Any thoughts?
Chris, why would your client, pay you to do the work you describe only to have it all pulled out when they say they are planning a rewire? seems like they are just wanting the work done and sid the rewire, watch yourself, could be a mess of trouble for you.
 

Reply to Working with wired fused ccu in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
543
8.5K shower unit is wired to plastic box consumer unit to 30 amp cartridge fuse with no RCD It’s the original shower installed when the house was...
Replies
19
Views
4K
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
631
Once again I am using the Engineering chat as I think my question is more theoretical rather than 'diy advice'. If I am misusing the forum...
Replies
17
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock