    I'm a bit stumped, feels like I'm hunting bigfoot. Anyone know a supplier for these?
     
  2. Gavin John Hyde
    Offline

    Gavin John Hyde Electrician's Arms

    Location:
    Somerset
    Business Name:
    Sulis Electrical Services Ltd
    whats the rcd/rcbo for ? if needed you could put a different brand in an adjacent plastic enclosure, rolec do type a rcbos for around £20 you might have to pay delivery but will be available from most wholesalers. they do 20 and 40 amp versions of the rcbo possibly other rated versions if you look
     
  3. Mattja
    Offline

    Mattja Regular EF Member

    Location:
    UK
    It's for a garage circuit with an EV point taken from the garage board, it's already in place but an EICR identified the AC type RCD isn't suitable. The board in the house is Wylex, put in about 2 years ago, so the simplest thing would be to have a suitable Wylex device to put in there.
     
  4. Ian1981
    Offline

    Ian1981 Forum Mentor

    Location:
    North east
    Only the rcd in the charging unit requires to be either a type A or type B rcd.
    The supply to the EV charger does not necessarily require rcd protection depending upon the installation method of the cable supplying it and whether fault protection is required by an rcd
    You also should not have a type AC rcd upstream of a type A or type B so is that what the issue is?
     
  5. Gavin John Hyde
    Offline

    Gavin John Hyde Electrician's Arms

    Location:
    Somerset
    Business Name:
    Sulis Electrical Services Ltd
    when installing an ev with a need for a type a rcd then i would usually install one in a seperate enclosure as the cost can be eye watering. hence why i sue rolec ones.
     
  6. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    • Like Like x 2
  7. Mattja
    Offline

    Mattja Regular EF Member

    Location:
    UK
    Cheers guys, had a glance at rolec, I think the answer is to modify the installation to take the supply to the EV point off the RCD.

    Fortunately for me the supply comes from the main DB to the garage DB is SWA, so I can modify the garage DB to have the other circuits in it on an RCD there. I personally prefer to have it RCD'd from the main board to have the cable run on an RCD too (regardless of it being a requirement or not, original installer was clearly like-minded), but changing that seems to be the only reasonable option here.

    A bit disappointed at the difficulty obtaining Type A rcds/rcbos. Even my accessor last time my scam paid a visit made it a point to say we should be looking for Type A due to the type of loads that are commonplace these days, but I can't install what I can't get hold of!

    P.S. Thanks Wilko but I'm pretty sure the B type there refers to the mcb (which also makes searching for a B type rcd/rcbo a huge pain as there's a ton of unwanted results).
     
  8. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - agree, these RCBO are type A RCD with a type B or C mcb.
     
  9. Electrical2go
    Offline

    Electrical2go Sponsor

    Location:
    UK
    Business Name:
    Electrical2go.co.uk
    • Like Like x 1
  10. Matthewd29
    Offline

    Matthewd29 Regular EF Member

    Location:
    Belfast
  11. Matthewd29
    Offline

    Matthewd29 Regular EF Member

    Location:
    Belfast
  12. Electrical2go
    Offline

    Electrical2go Sponsor

    Location:
    UK
    Business Name:
    Electrical2go.co.uk
    Hi Matthewd29,

    I'm sorry if we've missed an email from you.

    If you have any enquiries feel free to message directly on here and I will make sure it's followed through.

    Cheers,
    Ivan
     