jamminuk

Does an RCD need an earth to operate? I know it's additional protection and works on a balance between line and neutral but does it need earth to operate?

Thanks in advance

Ben
 
there has to be a path to earth on the circiut for the imbabalance to occur, but the RCD itself does not need an earth.
 
wel. yes. either through the cpc of the circuit, through damp, through your body. any path to earth will do
 
No, an RCD does not need an earth to work, but as above, current has to "leak" out of the circuit(s) protected by the RCD for it to operate. This leakage current is at the most 30mA (0.030 amps) before the RCD trips, although a healthy RCD will trip well within that. To clarify further, leakage current is, for instance, someone accidentally (or otherwise) coming in contact with a live wire in which case some of the current will flow through such person down to the earth. The RCD will then pick up that not all current leaving the line conductor is returning in the neutral and will thence operate because of this imbalance. Hope this helps too, I tried to make it simple but not sure if I've succeeded! Cheers
 
No, an RCD does not need an earth to work, but as above, current has to "leak" out of the circuit(s) protected by the RCD for it to operate. This leakage current is at the most 30mA (0.030 amps) before the RCD trips, although a healthy RCD will trip well within that. To clarify further, leakage current is, for instance, someone accidentally (or otherwise) coming in contact with a live wire in which case some of the current will flow through such person down to the earth. The RCD will then pick up that not all current leaving the line conductor is returning in the neutral and will thence operate because of this imbalance. Hope this helps too, I tried to make it simple but not sure if I've succeeded! Cheers

Yes mate that has made it clear thanks to you and telectrix, most helpfull and thanks for taking the time to help out, owe you a beer or two!!
 
If the RCD is of the conventional mechanical mechanism and toroidal transformer construction, it does not require a functional earth for the device itself to operate, but its final circuit does require a CPC.
If on the other hand the RCD is of the all electronic construction (like most RCBOs), it will require a functional earth to provide a reference for the electronics to operate, plus its final circuit will require a CPC.
 
Last edited by a moderator:
had this question myself many moons ago, tried testing the rcd with main earth disconected and it it still tripped under test so theoretically no an earth is not required but some form of earth path must exist for enough current to leak to create an imbalance.
 

Reply to Yet another RCD question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
718
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer...
Replies
1
Views
1K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K
I have a bathroom fan with a moisture detector that turns it on and off. It also has a control circuit to turn it on/off when moisture is not...
Replies
1
Views
250
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
542

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock