Hi all just a quick question carried out all of the above tests yesterday and got the following results

Ze . Tncs system 0.18 which is fine
Pefc . 1.1ka
Psc . 1.6

Carried out the same tests today and got these results

Ze 0.28 again fine
Pefc. 845 amps
Psc 1.1ka

Can anyone tell me why these readings are different and does it matter as they are all still acceptable reading for the protective device.

Thanks chris
 
does that mean that due to fluctuations an installation could fail so it should be tested a few times before contacting the DNO?
 
Could it be due to how much power had been drawn before testing. If day one nothing had been on, then the conductors would be cool and resistance low, on day two if there had been a high load on the conductors prior to testing, the heat in the conductor may create a higher resistance?
 
I would not consider contacting the DNO, untill I had obtained a number of consistant measurements.
To be honest there are a number of reasons why you could have the discrepancy.
Poor connections of the probes, loads not disconnected, voltage spikes, voltage lows. Possibly even an increase in the capacitive reactance due to loads on the communal cable, from other installations.
 
I would not consider contacting the DNO, untill I had obtained a number of consistant measurements.
To be honest there are a number of reasons why you could have the discrepancy.
Poor connections of the probes, loads not disconnected, voltage spikes, voltage lows. Possibly even an increase in the capacitive reactance due to loads on the communal cable, from other installations.

Or more likely, some's not learned how to zero their meter.
 

Reply to Ze.pefc.psc testing. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
787
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
828
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock