Discuss Zs ohms with maximum rcd ohms in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Wilson12

-
Trainee
Reaction score
3
If the maximum zs is okay up until 1667 ohms protected by a rcd why do we care about maximum disconnection times for the mcbs e.g why do we test and it's important to meet 1.37 or 1.1 zs on a 32 amp circuit
 
If the maximum zs is okay up until 1667 ohms protected by a rcd why do we care about maximum disconnection times for the mcbs e.g why do we test and it's important to meet 1.37 or 1.1 zs on a 32 amp circuit
because we should aim for fault protection to be provided by the OCPD, not reliant on a RCD.
 
If the maximum zs is okay up until 1667 ohms protected by a rcd why do we care about maximum disconnection times for the mcbs e.g why do we test and it's important to meet 1.37 or 1.1 zs on a 32 amp circuit

Not all circuits are protected by RCD.
The regulations don't allow RCDs to be used as the sole means of protection, they are only additional protection. So you need to ensure that protection is provided by the ocpd.
 
No this is just me wondering.im doing a eicr around the house and worrying about high zs readings looking for loose connections and I'm wondering why is the regulations even there to abide by.i can't think why it matters if the readings are over the maximum zs readings as theirs a rcd split load preotecting them .
 
If it's a split load board is there any reason to worry if the zs readings are higher then the mcbs specified
Well if it's a TN type earthing system , you got to wonder why the zs readings are high?
You will of course be covered by a dual rcd consumer unit providing the necessary fault protection for your 0.4 or 5 second disconnection times
 
Well if it's a TN type earthing system , you got to wonder why the zs readings are high?
You will of course be covered by a dual rcd consumer unit providing the necessary fault protection for your 0.4 or 5 second disconnection times
not the point. using the RCD as fault protection is at best a fudge, and at worst, dangerous. a circuit that should give a Zs reading of, say, sub 1.0 ohms and has a reading of 4.0 ohms may have a bad connection that could lead to arcing and a possible fire risk.
 
not the point. using the RCD as fault protection is at best a fudge, and at worst, dangerous. a circuit that should give a Zs reading of, say, sub 1.0 ohms and has a reading of 4.0 ohms may have a bad connection that could lead to arcing and a possible fire risk.
Not disputing that , just that there will be fault protection afforded by the rcd, I did say you've got to wonder why you have a high zs reading on especially a TN system
 
I would look at it from the point of view of considering a similar situation with the line and neutral loop.
Even though we do not test for this is you have a high line neutral loop impedance then the MCB may not disconnect in time to protect the cable, measuring the Zs at least measures the line side of the loop.
If the Zs is high this may be from circuit design limitations or from errors in installation, if it is errors then you can make attempts to correct, if it is from design limitations then it gives you the chance to assess whether the circuit will comply with the requirements of 434.5 and meet t= (k²S²)/I² (which is just a rearrangement of the adiabatic equation to allow you to determine maximum disconnection times).
 
Use the alternative Zs method a bypass the RCD! You may see the results drop using this method on hi current test.

No this is just me wondering.im doing a eicr around the house and worrying about high zs readings looking for loose connections and I'm wondering why is the regulations even there to abide by.i can't think why it matters if the readings are over the maximum zs readings as theirs a rcd split load preotecting them .
 
Just an expansion on this.

Do you allow any tolerance on the max recorded Zs? I.e. 0.61 ohms on when max zs is .55 this is based on the 80% rule and not the maximum permitted zs
 
The 80% factor is a good estimate of copper resistance at 70C when remeasured at 20C. So it's not a tolerance.
The BS7671 tabulated values will have the conductor temperature stated, and it's often 70C. We tend to test and measure when a circuit is at room temperature and so we multiply by 0.8 to get an equivalent value.
 
The 80% factor is a good estimate of copper resistance at 70C when remeasured at 20C. So it's not a tolerance.
The BS7671 tabulated values will have the conductor temperature stated, and it's often 70C. We tend to test and measure when a circuit is at room temperature and so we multiply by 0.8 to get an equivalent value.
I think I have probably misinterpreted your words, but the proximity of the 80% appears to refer to correcting a measured resistance to a 70°C resistance.
Whereas it is the 70°C resistance that is multiplied by 0.8 to give an value close to the expected measured resistance at 20°C.
Or alternatively the resistance measured at 20°C is multiplied by 1.2 to give the expected resistance at 70°C
 

Reply to Zs ohms with maximum rcd ohms in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Does a RCBO protecting a single circuit mean it can have a maximum Zs of 1667 Ohms since it's being used as fault protection?
Replies
3
Views
3K
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock