Have measured R1 + R2 and get a total of .45 ohms, when I test the ring with my tester I get 2.1ohms, the unit was calibrated last week, any ideas?
 
what's the Ze? and if it's a sub main, the Zdb?
 
What are yor r1, rn & r2 readings on the ring? Ze or Zdb readings? Is this circuit protected by a RCD or RCBO?
 
Ze is .27, the sleeving is not trapped, the circuit is RCd protected, not that makes any difference to the reading at the sockets, the test lead is a kettle type.
 
You could find that it is the RCD that has the high impedance. Try a loop impedance test both sides of the rcd and see if it differs.
 
The current crop of 2 lead no trip meters give totally unreliable readings as well.....worth bearing in mind if you are testing with one of those.
 

Reply to ZS on final sub circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock