At a property today I found that several lights have been taken as a spur of a ring main. At the end of the spur I get 1.33 Zs which is too high as it's on a 32A B MCB and should be lower than 1.16.

If I convert this to a fused 3A spur with FCU, can I used the 3A fuse to calculate the max Zs allowed? (which would be OK if so)
 
Yes that would be ok.
 
your Zs would be for the circuit from the fcu to last light and if a 3amp fuse is ok load wise then thats what you should use
 

Reply to Zs on lights spur of ring in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock