Discuss Zs Problem in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hey folk. i have been doing some testing and up to now i have had no problems. however today i have been getting a reading of >2000 ohms when doing a Zs test. i have been searching my brain and evrything else for a reason for this but cant find anything. this reading i am getting is right through the whole installation from the individual DB right back to the Main panel. would really appreciate it if anyone has any reason behind this. thanks.
 
What was the Ze/Zdb reading?.....if it's across the board it suggests a loss of main earth. Is the meter working correctly as well?
What is the purpose of this test....I hope it's not an EICR....if you cant work out a high Zs reading?
 
getting the same at the main panel. its powered by a generator and everything was fine yesterday so i am unsure as to how this has happened today.
its an installation for camp accommodation.
 
what is the ambient temperature at the time of test, and the max operating temperature of time of test, it say s both of which will have an effect on conductor resistance
 
earth rods are intsalled around the gene. i am in afghanistan working and the ground isnt very good for getting a good Ze but i was still getting 0.15 ohms yesterday as a Ze reading so how this has changed overnight is beyond me
 
lol @ Mark. aye you're probably right. well it is somehow managed to rectify itself and i am now getting a Ze reading well within what it needs to be. think it might have been an issue with the meter but whoknows. thanks for your help guys.
 
earth rods are intsalled around the gene. i am in afghanistan working and the ground isnt very good for getting a good Ze but i was still getting 0.15 ohms yesterday as a Ze reading so how this has changed overnight is beyond me


I would have to beg to differ, if your getting Ra/Ze readings of 0.15 ohms!!!! ..lol!!!

I bet they're not using the short 3/8'' twigs for they're earth electrodes, more like the 10 foot 5/8'' or 3/4'' proper earth rods, and linking a good few of them out too...lol!!!
 

Reply to Zs Problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
473
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
229
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
472
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
380
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock