B

beaver74

Hi all

with a heathy ZE ..22 on a TN-s system i had a R1+R2 of .40 oh my suprise to find that the Zs was 1.01at the furthest socketrechecked my ZE.22??
rechecked ZE from out going terminals of RCD .60 has any one else found this

ps i realise that this reading is fine as RCD protected just wondering
 
Hi all

with a heathy ZE ..22 on a TN-s system i had a R1+R2 of .40 oh my suprise to find that the Zs was 1.01at the furthest socketrechecked my ZE.22??
rechecked ZE from out going terminals of RCD .60 has any one else found this

ps i realise that this reading is fine as RCD protected just wondering

No trip or D lock setting on the meter by any chance
 
Ya I've seen this too, several times. But sometimes this internal resistance of RCCB is really high. Mostly it's about 0.20ohm to 0.30ohm but in some occasions it's 0.50~0.60ohm. RCBOs have less in my experience. I mentioned this issue in IET forum couple of months ago and outcome was it's normal, nothing to be worry about. But is this this really ok or not, you should judge yourself. :)
 
Ya . But is this this really ok or not, you should judge yourself. :)
as for the reading no problem in the higher Zs as it is protected by the RCD .but i was more concerned about the fact you can have such a differance acroos what is in effect a swithed set of contacts
 
Always get a slightly higher reading when using the no trip function as opposed to the high current loop test.
 

Reply to Zs reading across RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock