nursa

my supervisor told me, recently, that zs readings on a tt system do not have to comply with the maximum zs figures in the regs. i have always worked to max zs figures no mater what system. whose right?
 
Your maximum permitted is 1667 ohms over 200 ohms it may be unstable NICEIC recommend 100 ohms. Remember that BS 7671 is guidance so not legally enforcable despite the fact that they will quote BS 7671 in a prosecution against you, so I treat BS7671 as a legal requirement.




Chris
 
ive recently tested a tt system and got 0.25 ohms ze. when testing zs on all circuits my readings are in the region of 260 ohms. this fails the test?
 
when you test the ze the best way to get a pure reading is to remove the main earth from the cu
then test onto the end of the cable
as chris said aim to get 100-200 ohms
then replace and test zs readings these may be lower due to better earth paths through bonds etc

your .25 reading is very low and there maybe something else causing this
 
Last edited:
yup it was disconnected for test. also tested gas and earth bonds getting 0.3.and 0.29 respective. cant figure out why zs readings so high. new ccu, connections all good. havent checked every termination in property but ring, lights, cooker and single spured socket all too similar to think this is the problem.
 
Seems very strange that Zs readings are so high. You might want to check the busbar has gone into the bottom of the RCDs properly. I've been caught out with thinking it was screwed in tight and got no power. The busbar had gone in front of the screw instead.
 
Ze on TT at 0.25....not a chance.

The lowest I've ever heard of was on a job I did a while back in a quarry, we ran 120mm earth on to 9 sets of 2x14mm copper rods on a grassy bank with bentonite in the hole and we only got 4.22ohms then!

Surely your mistaken??:confused:
 

Reply to zs results on tt system in the Australia area at ElectriciansForums.net

Similar Threads

Now Ive done Periodic Inspection and Initial Virification Qualifications with LCL/EAL (so non C&G 2394/95) # strange part building Modules , this...
Replies
6
Views
936
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi everyone, Happy Friday! Could someone please point me in the right direction, I’m after the Max Zs for a Bill Talisman TLF633 63A MCCB, I’ve...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock