Zs, Ze how the tester works?

Discuss Zs, Ze how the tester works? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
34
I understand how to test Ze and Zs and that Zs is the total impedance from the suppliers tranny to the final accessory in a circuit your testing. Also that Ze is the suppliers earth resistance.

However i have a few questions

1.) how does the test meter actually work to measure Ze by connecting the meter to the main earth (obviously main earth disconnected from MET) and to the phase conductor? does it link it out or send a current or what?

2.) Why and how does Zs effect a devices tripping time? like what is the theory behind it. I know Low Zs means that fault current will be higher thus tripping the device but how does it trip the device and what device MCB ? RCD? how does fault current going down earth trip a MCB?

3.) Would you be able to just do a test from the main isolator in the disboard and record that measurement for all the Zs readings (adding Ze reading off course) on different circuits or does it have to be done individually for each circuit to get the furthest point in the circuit?

4.)Does the meter measure prospective fault current by just using ohms law and dividing mains voltage by resistance of the cable but what i dont understand is how does the meter find the resistance of the cable does it pull a load on it and then calculate or what?


Thank you for your time
 
9
firstly MCB and rcd do different jobs ,so if you asking about tripping RCDs when doing efli tests that cool or if you asking why we have maximum zs for tripping times that fine too , it just your overloading your self with questions and adding them together so it doesn't make sense when your responding , if we got off on the wrong foot sorry ,i always said i wouldnt do the "get a electrian in , that under part P etc response s so it my bad
I know mate i wasnt very clear we were just discussing the topic in college for our test and inspect exams so had a lot of clearing up that needed doing. I was asking why we have maximum Zs for tripping times and how an MCB or RCD would trip any quicker with lower Zs.
 
makes sense mate thanks
Another example for touch voltage would be take a bathroom with just a lighting circuit 6 amp type b mcb not rcd protected but supplementary equipotential bonding has been carried out.
If you wanted to test the affectivness of the bonding then a continuity test between exposed pipework and the cicrcuits cpc would need to be within 1.67 ohms before the max 50v touch voltage is exceeded as the formula would be 50v/ 30amps (to trip a 6amp type b mcb ) = 1.67 ohms.
 
Another example for touch voltage would be take a bathroom with just a lighting circuit 6 amp type b mcb not rcd protected but supplementary equipotential bonding has been carried out.
If you wanted to test the affectivness of the bonding then a continuity test between exposed pipework and the cicrcuits cpc would need to be within 1.67 ohms before the max 50v touch voltage is exceeded as the formula would be 50v/ 30amps (to trip a 6amp type b mcb ) = 1.67 ohms.
Another example for touch voltage would be take a bathroom with just a lighting circuit 6 amp type b mcb not rcd protected but supplementary equipotential bonding has been carried out.
If you wanted to test the affectivness of the bonding then a continuity test between exposed pipework and the cicrcuits cpc would need to be within 1.67 ohms before the max 50v touch voltage is exceeded as the formula would be 50v/ 30amps (to trip a 6amp type b mcb ) = 1.67 ohms.
Ian, sorry I'm confused, where did the 30A come from in your calculation? I may have missed something, hence my question
 
A 6amp type b mcb will trip instantaneously at around 3-5x rated current.
6amp x 5 is 30amps for type B.
That's where the 50v/ 30 comes in for that particular type of mcb.
As the max zs is 7.28 ohms on a 6amp mcb type b it's 230x cmin 0.95=218.5volts /30amps=7.28 as this is max zs value for the mcb.
 
There are as Westward said, two parts to an MCB.
The magnetic and the thermal.
The thermal part and fuses work because they get hot.
Fuses get hot and melt.
MCBs have a bi metal strip which heats up and bends until it trips the switch mechanism.
The bi metal strip is made up of two metals which expand at different rates, as the strip heats up it bends towards the side which has the metal with the lowest expansion rate.
This is similar to an indicator relay in a car or motorbike.
 

Reply to Zs, Ze how the tester works? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock