Currently reading:
3 Phase Metering Question

Discuss 3 Phase Metering Question in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Good morning,

So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their pool.

So currently looking at possibly using MyEnergi Eddi’s or something similar to power a 3 phase heater element (probably split into 3 single phases) and the pool pump.

I’m not really up on how 3 phase metering works and if it’s different in a domestic installation either.

If we went the 3 phase route and the phases are unbalanced (e.g. phase 1 is exporting, phase 2 is exporting but phase 3 is importing) and the sum of all phases mean that there is a net export would you still pay for the energy that is imported on phase 3?
Or does the meter just see a net export so doesn’t count up additional units?

Obviously if this isn’t the case it will have to be 3x 1-P elements to make the largest benefit from the solar.

Any help appreciated.
If anyone has done something similar and has any insight into how they did it that would be great too.

Thanks!
 
ALl depends on whether the inverter can handle asymetrical output ie if Ph1 needs more than Ph2 or 3 it will export ACpower accoding to need, some older inverters chuck out the same across all 3 phases.

As far as I am aware Eddi only handles single phase loads - however I have seen an Eddi wired to a contactor to then switch much bigger loads.

I believe the new 3 phase smart meters group the cumulative import / export so it doesnt really matter what phase the use/export is on. it all gets added together
 
ALl depends on whether the inverter can handle asymetrical output ie if Ph1 needs more than Ph2 or 3 it will export ACpower accoding to need, some older inverters chuck out the same across all 3 phases.

As far as I am aware Eddi only handles single phase loads - however I have seen an Eddi wired to a contactor to then switch much bigger loads.

I believe the new 3 phase smart meters group the cumulative import / export so it doesnt really matter what phase the use/export is on. it all gets added together

I’m pretty sure the 3 phase inverter is just equally splitting it between phases, or it would seem so from the power analysis.

Yeah they do only handle single phase loads. So it’s rather have 1 Eddi connected to a contactor to bring on the 3 phase heater element and assume equal loaded (exporting) phases (probably causing some import at times but it should even out if the right phase is being monitored by the Eddi).

Or, 3 separate Eddi’s on separate phases sending out variable power (depending on export at that time) to each of the elements of the 3 phase heater (rewired as 3x 1P elements).

Obviously the first option is easier and cheaper but for some reason I was thinking if 1 phase was exporting and 1 phase was importing, with a net import, then the meter would be racking up units from the phase which is importing.

Not sure why I thought that this morning, think I was thinking pF, but again that doesn’t apply to domestic… must be losing it.

Thanks
 

Reply to 3 Phase Metering Question in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top