Search the forum,

Discuss Advice on Isolator Switches needed please in the DIY Electrical Advice area at ElectriciansForums.net

D

Deleted member 155212

Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the future I might need a 7.4kW/32A charging point and the garage isolator is only 60A.

1. Recently, during a kitchen refurb, double pole Mains Isolators were fitted in the Meter Enclosure - image 1. 25mm2 'tails' were fitted because the incoming power was upgraded to 100A.
2. Inside the garage, opposite the Meter Enclosure, the new 'tails' are connected to an old MEM Isolator Switch - image 2. That Isolator switch has a ceramic re-wirable fuse and that fuse is only rated at 60A.
3. The armoured cable from that MEM Isolator Switch goes to a new, metal, split load Consumer Unit inside the house - image 3. Naturally that Consumer Unit has another Mains Isolator Switch.

The oldest part of the installation is the MEM Isolator Switch. I am having trouble finding a ceramic MEM re-wirable 100A fuse and am not sure that is the best solution anyway. So my questions are:

1. Do I actually need the MEM Isolator Switch in the garage if the Meter Enclosure and the Consumer Unit both have isolator switches?
2. Could that MEM Isolator Switch just be removed OR should it simply be replaced with a 100A cartridge type fuse OR a suitable 100A breaker?
3. "One day" I will need to fit a Charging Unit for a car and the location of the MEM Isolator Switch would be a good point to take a cable through the garage wall to the outside for that charging point. So what would that arrangement look like? Would it be a very small 'Consumer Type' unit with an isolator switch plus a 32A 'take off' connection for the charging point?
4. OR should the power for that charging point come from the new 'Consumer Unit' inside the house (i.e. the unit in image 3)? It seems odd to take the power all the way to the Consumer Unit in the house and then cable it all the way back to the garage.

Apologies for some of the terminology. Any help and advice would be greatly appreciated. Thanks for your time.
image 1.jpgimage 2.jpgimage 3.jpg
 

Reply to Advice on Isolator Switches needed please in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
773
I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
909
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock