DPDT switching branch circuit from one breaker to another?

Discuss DPDT switching branch circuit from one breaker to another? in the UK Electrical Forum area at ElectriciansForums.net

rmully

DIY
Reaction score
6
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor can be #10, and a 30A breaker is probably OK, but a 40 would help the duty cycle. Conductor must handle welder's 1eff rating, breaker can be up to double 1max rating.

I have a dedicated 240V, #10 conductor, 30A breaker circuit in place. I don’t want to modify that by upping the breaker size and making it unusable for other things, and I’d rather not run a long, entirely new circuit, wanting to save $ and not run a lot of new wire, conduit or wire mold through the space and on to an exterior wall.

I have on hand a few feet of #10 wire, and a 30 amp 120/277 volt 3 position toggle DPDT wall switch.

Is this OK or stupid: install a new circuit, 240V, #10 wire, 40 or 50A breaker, running to a new junction box about a foot or so from the panel. Sever the cable of the existing aforementioned circuit and run it into that box. Now there are two circuits running into the junction box, both with #10 wire, one with 30A breaker for conventional uses, and one with the upsized breaker for welder only. Then install the 30 amp 120/277 volt toggle DPDT wall switch in the box, connecting it to the existing branch circuit that continues on through the building. I could mark the switch plate something like WELDER and OTHER, and switch between the two as needed.
 
Here's a diagram of what I'm trying to describe.

Unless I'm mistaken, depending on a welder's 1eff and 1max rating, code for a dedicated, single welder branch circuit may use #10 wire with a 50A breaker.

I have a 240V, #10 conductor, 30A breaker branch circuit in place. I don’t want to change that by upping the breaker size and making it unusable for other things.

So I'm wondering if I can make a new circuit, same wire size but with a 50A breaker and switch between the two with a DPDT switch.

I have spare wire, a DPDT switch and 50A breaker so it's an inexpensive job.




DPDT DIA.jpg
 
It sounds bonkers.

If the socket is only rated for 30A then that should be the maximum breaker size. If you have very high surge peaks then you can get breakers with a higher magnetic to thermal ratio (for example D-curve MCB instead of typical B-curve or C-curve in most EU/UK boards), but in UK regulations you have to ascertain that it will disconnect under fault conditions fast enough so a low enough earth loop fault impedance. I'm not familiar with USA code to advise on these aspects for you, but someone like @Megawatt will know far more.

If you need a 50A socket for the welder just put one in. It is likely not much more expensive than the switch and box, etc, needed above and you might find a use for both sockets at once.
 
I think the root of my question is easily obscured by the uncommon aspect of code for welders.

Many welders have two ratings - I 1eff, and I 1max.
I'm looking at one unit that is rated at 25A I 1eff, and 35A I 1max.
By code, a single dedicated circuit for it can be #10 with a 40 or 50A breaker.
Given that, I have two questions:
1) If for welders, #10 wire is OK with a 40A breaker, wouldn't a 30A switch be OK within that circuit? It's the same capacity as the wire on either side of it.
2) is the overall idea to switch between two circuits OK?
It seems doable and safe to me.
 

Reply to DPDT switching branch circuit from one breaker to another? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock