Currently reading:
Why is split RCD not appropriate for TT?

Discuss Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

It doesn't say that on the link you provided, either. So where are you getting the quote from?

The only rebuttal to what the regs clearly says has so far been something that's not in the regs at all. IMO it confuses things greatly. Could we stick to what's in the actual brown book instead of someone else's interpretation of it? Think it would help fuel the discussion instead of confusing matters.
 
With RCBO's the supply is via the busbar. It's in a fixed position so can't come into contact with the casing.
Just thought I'd offer another perspective on this:

The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.

This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.
 
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
I can't find where it is and i haven't got the book, but it says:

“Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this”
 
Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.

Things are starting to get a bit confusing, what quoted reg have I said isn't correct ?
 
Just thought I'd offer another perspective on this:

The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.

This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.
The same could be said for a dual RCD board.
 
I can't find where it is and i haven't got the book, but it says:

“Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this”
It doesn't, i've searched an electronic version of the regs and that's not in there.

The reg i quoted was written verbatim from the book.
 
Just thought I'd offer another perspective on this:

The busbar is fixed, but uninsulated, in an enclosure containing a number of sleeved CPCs. Sleeving, I'm told, is for identification only and isn't officially rated as an insulator (though real world I'm pretty sure it does offer some level of insulation). Anyway, the uninsulated CPCs could make contact with the uninsulated busbar, resulting in a L-E fault that won't disconnect.

This makes me think that this risk for TT installations is possibly worse for an RCBO board, vs a dual RCD board, where the cables feeding the RCDs at least have proper insulation.


I think that the cables feeding the rcds are the problem, not the busbars.


Regulation 531.3.5.3.2.201 requires that, where Class I enclosures are used (that is, earthed metalwork) on TT systems with RCD protection on outgoing circuits, all live conductors on the supply side of the RCD – that is, the internal cable links – must have double or reinforced insulation.


As each RCBO is supplied by a busbar, the risk of the busbar becoming loose and making contact with the metal enclosure is minimal.
 
It doesn't, i've searched an electronic version of the regs and that's not in there.

The reg i quoted was written verbatim from the book.


Yes you're using that quote as the basis for saying the quoted reg isn't 100% correct but the quote doesn't appear anywhere in the regs.
Like I said earlier, I'm a bit confused as to what part of the regs I'm saying is wrong ?
I only have the 17th edition green book to hand, but it's certainly in there.

537.2.1.2 : Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this
 
Like I said earlier, I'm a bit confused as to what part of the regs I'm saying is wrong ?
I only have the 17th edition green book to hand, but it's certainly in there.

537.2.1.2 : Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this
It appears to have moved in the 18th to 422.3.13:

422.3.13
Except as permitted by Regulation 461.2, every circuit shall be provided with a means of isolation from all live supply conductors by a linked switch or a linked circuit-breaker. NOTE: Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this.
 
It appears to have moved in the 18th to 422.3.13:

422.3.13
Except as permitted by Regulation 461.2, every circuit shall be provided with a means of isolation from all live supply conductors by a linked switch or a linked circuit-breaker. NOTE: Provision may be made for isolation of a group of circuits by a common means, if the service conditions allow this.
I stand corrected.

So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.

The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.

No wonder the rest of the world laughs at our electrical practices.
 
Last edited:
I stand corrected.

So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.

The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.

No wonder the rest of the world laughs at our electrical practices.

But if everything was as clear as glass, there wouldn't be forums like this where gentlemen discuss these things in a friendly, happy manner. 😇
 
Last edited:
But if everything was as clear as glass, there wouldn't be forums like this where gentlemen discuss these things in a friendly, happy manner. 😇
Hey it's been a good discussion i think!

My problem was i thought you were referring to the sentence being in the same reg, i didn't know it'd be in a completely different part of the book!

I doth my cap to you; you were right.
 
I stand corrected.

So it's a case of EVERY circuit SHALL be provided with a means of isolation, except for when they aren't. And make sure you don't read the other contradictory rule about this in a completely different section of the book where it says each individual circuit must be individually switched. Clear as custard once again.

The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.

No wonder the rest of the world laughs at our electrical practices.

There aren't as many errors or contradictions in BS7671 as you seem to think.
There is often more of an issue with people not reading it properly, not understanding the language used and sometimes people will just read what they think is written and not actually what is there.

Where in the rest of the world are our electrical practices laughed at? We are far ahead of a lot of countries in electrucal safety and standards
 
The more i read these books the more i think the IET aren't fit for purpose - contradictions, ambiguity, spelling errors abound. Even some of their very important equations needed for testing are wrong in the books.
A more general point...
It's very difficult to take the 'painting by numbers' OSG (which is a simplified set of rules that can be followed exactly to comply with BS7671) and then try and work backwards to BS7671. Trying to guess the full version from a particular method of complying is almost like trying to reverse engineer the regs.

I took a break from the industry during most of the 17th edition era, and hence fairly recently did an 18th edition course. I was actually strongly advised to NOT read the OSG until I'd passed the exam, as the layout and manner in which it sets out things is not conducive to learning the regs. I think it was good advice!

The brown book for all it's complexity is laid out in a certain structured way, and learning to think in terms of this structure is the best way forwards. So I guess what I'm saying is that should be where the focus goes.

(I'm far from an expert on the regs, but I believe I understand the structure and then it's a case of slowly filling in the blanks!)
 
A more general point...
It's very difficult to take the 'painting by numbers' OSG (which is a simplified set of rules that can be followed exactly to comply with BS7671) and then try and work backwards to BS7671. Trying to guess the full version from a particular method of complying is almost like trying to reverse engineer the regs.

I took a break from the industry during most of the 17th edition era, and hence fairly recently did an 18th edition course. I was actually strongly advised to NOT read the OSG until I'd passed the exam, as the layout and manner in which it sets out things is not conducive to learning the regs. I think it was good advice!

The brown book for all it's complexity is laid out in a certain structured way, and learning to think in terms of this structure is the best way forwards. So I guess what I'm saying is that should be where the focus goes.

(I'm far from an expert on the regs, but I believe I understand the structure and then it's a case of slowly filling in the blanks!)
A lot of sense in that approach.

The OSG is not so much a guide to the regs as a simplified set of standard installation methods that will comply (within the limitations given).

It's also true though that the Regs have become a bit of a behemoth, partly because of the way additions and notes have been added to 'clarify' things, to the point where it is not always clear what the requirements actually mean.

It's not helped by the interconnection between it and many other standards, which most people have no access to due to cost.

Then you have the various electrical bodies guidance put out which doesn't always agree or in some cases is conflicting, leading to unnecessary confusion.
 

Reply to Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock