The DP main switch makes it compliant.I know that but OSG is supposed to be a bite-sized, easy reference for whats in the big brown book. Seems like the OSG talks a lot of gibberish.
Here's another one.
OSG page 61.
'Other than at the origin of the installation, every circuit...that may have to be isolated without interrupting the supply to other circuits should be provided with its own isolating device. The device must switch all live conductors in a TT system and all line conductors in a TN system.'
This basically says all breakers have to be double pole in a TT, no?
Yet you go to 132.15.201 which the OSG references and it says absolutely nothing about this.
Which reg is that?Regulations now require residential to be rcbos.
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.The DP main switch makes it compliant.
It does mention 'without interrupting the supply to other circuits'.The DP main switch makes it compliant.
But that reg says supply side of the incoming device eg main switch. **** me these books are confusing. Someone should rewrite them in normal language, they'd make millions.Think it stems from
Regulation 531.3.5.3.2.201
It does also mention the internal wiring I think. Says something about them being double insulated orBut that reg says supply side of the incoming device eg main switch. **** me these books are confusing. Someone should rewrite them in normal language, they'd make millions.
Only as it pertains to a pre-assembled board's link cables as far as i can see.It does also mention the internal wiring I think. Says something about them being double insulated or
reinforced.
531.3.2 (ii)Which reg is that?
'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.Only as it pertains to a pre-assembled board's link cables as far as i can see.
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.
I'm sure it says somewhere “that provision may be made for isolation of a group of circuits by a common means”It does mention 'without interrupting the supply to other circuits'.
The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.531.3.2 (ii)
It does say 'considered'.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double'Regulation 531.3.5.3.2.201 requires that where Class I enclosures are installed in installations forming part of a TT system and RCD protection is used on outgoing circuits, all live conductors on the supply side of the incoming device must have double or reinforced insulation'.
Taken from NICEIC website.
It doesn't, not in that quote from the OSG anyway.I'm sure it says somewhere “that provision may be made for isolation of a group of circuits by a common means”
Welcome to the world of interpretation.It doesn't, not in that quote from the OSG anyway.
It's all terribly confusing.Welcome to the world of interpretation.
You were asking about the main tails and argued that :-The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.
NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.
From the book.
Supply side of eg main switch is massively ambiguous imo.
I was merely pointing out that it does mention DI tails or reinforced insulation.Only as it pertains to a pre-assembled board's link cables as far as i can see.
That quote though says that all individual circuits must have their own DP isolating device. Yet the regs don't mention it.
It doesn't say required it suggests them.The same reg also mentions split RCD though so i don't think it means RCBO's are required in residential premises.
For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double
or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the
incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the
requirements of double or reinforced insulation.
NOTE 1: When selecting equipment, consideration should be given to the assembly manufacturer's internal line interconnecting
cable links on the supply side of an RCD being insulated and non-metallic sheathed, or having reinforced insulation
or equivalent mechanical protection.
From the book.
Supply side of eg main switch is massively ambiguous imo.
Nah i'm on about the load side of the main switch to the supply of the RCD's which is what the picture in OSG shows.You were asking about the main tails and argued that :-
I was merely pointing out that it does mention DI tails or reinforced insulation.
You said RCBO's were now required in residential installations.It doesn't say required it suggests them.
Reply to Why is split RCD not appropriate for TT? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net