Currently reading:
4 Core SWA linking two legs of a ring circuit

Discuss 4 Core SWA linking two legs of a ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Hi folks, I'm recently qualified so be nice...

I'm preparing a quote for the wiring of a dozen up and over garages which are in two rows of 6 and face each other with an 11m gap. One double socket per garage and fcu for a single 1500 fluorescent fitting. I was planning to wire them all as one ring circuit and use swa 2.5mm 4 core to link the two rows. Singles and pvc conduit for the wiring in each row of garages and then wiska box for the connection to the swa.

The armour would be the cpc so it wouldn't be a ring as such. I couldn't find anything in the regs which says it's a no no but I'm open to anyone opinions on this. It's obviously cheaper than running 2x 2.5mm swa cables but would it still be classed as a ring circuit?
I was hoping to use this job for my part p assessment so it has to be a perfect job. Feedback welcome.

Thanks!
 
'If in doubt put a spike in' is a cop out used by too many sparks, if you are at the start of your career, please don't fall into this lazy mans trap. Caravans, long runs to buildings/structures with pipework etc in and agricultural buildings with a lot of metal stuff about are a different ball game, all have their different reasons for not extending the equipotential zone to them and each case should be considered on an individual basis, not just 'come on billy lets knock a rod in'

I know it's hard to find work when you first start out and you don't want to turn anything away but this job has all the hallmarks of a pain in the buttocks for you and not something you need when you are trying to get yourself off the ground. Not having a go chap, just offering some friendly words of advice.
 
The point about faults above is quite important.

There will inevitably be a freezer in one or two of these garages. So when someone else uses something in their garage which trips the RCD on Saturday morning and the electrician comes out to investigate on Monday, who's going to pay for the contents of the freezers?
 
Well that's an interesting point, would it also make no difference on a TNCS system? (Gaps in my earthing system knowledge showing here...) Although with an rcd protecting the circuit the max Zs could be up to 1667 ohms and still comply in theory. Not that anyone would find that acceptable!

Adding a decent earth rod/nest connected to the MET of a TNCS system has it's advantages and is advisable in some situations but still won't help the Zs values in the installation.
 

Reply to 4 Core SWA linking two legs of a ring circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock