I have just watched one of John Ward's interesting videos -
It all makes sense apart from one of the final points involving adding an earth rod to an existing TN system. Not making a TT, but using the rod in addition to the TN system. This part is at 20 minutes and 8 seconds if you want to skip to it.
In relation to a broken PEN conductor he mentions that a suitably low Ra would be required for this rod to be of use. He mentions 10Ω's or less. He then says it may need to be 4Ω's or less if you have a substantial load on the system (i.e EVCP). I realise this is so a dangerous voltage is not reached but I cannot see how that relates to his figures of 10Ω and 4Ω.
For example. Lets say we have 20A (not even a substantial load) flowing throw the system (with a PEN fault) and we have a rod with an Ra of 10Ω
Using V = IR
V = 20 x 10 = 200V
I realise I must be using ohms law in the wrong context here as if the load was 40A the equation gives 400V which is impossible on a single phase system. Confusing!
It all makes sense apart from one of the final points involving adding an earth rod to an existing TN system. Not making a TT, but using the rod in addition to the TN system. This part is at 20 minutes and 8 seconds if you want to skip to it.
In relation to a broken PEN conductor he mentions that a suitably low Ra would be required for this rod to be of use. He mentions 10Ω's or less. He then says it may need to be 4Ω's or less if you have a substantial load on the system (i.e EVCP). I realise this is so a dangerous voltage is not reached but I cannot see how that relates to his figures of 10Ω and 4Ω.
For example. Lets say we have 20A (not even a substantial load) flowing throw the system (with a PEN fault) and we have a rod with an Ra of 10Ω
Using V = IR
V = 20 x 10 = 200V
I realise I must be using ohms law in the wrong context here as if the load was 40A the equation gives 400V which is impossible on a single phase system. Confusing!