Currently reading:
New Zealand Connect 2 Separate Switches to Operate 1 Light

Discuss Connect 2 Separate Switches to Operate 1 Light in the UK Electrical Forum area at ElectriciansForums.net

Arborist

DIY
Reaction score
0
Hi everyone, I'd like to say hi as this is my first post.

Along with many other folks out there, I have been making use of the lock-down time to get on with some DIY projects. One of these is to change the dated spot light wall fitting over the bed. It has 2 spots, each operated by a separate switch. My new fitting still has 2 spots, but only 1 connection. Can I just join the wires coming from the 2 switches at the light fitting (see photo). Cheers and all the best, Tim
 

Attachments

  • 20200609_121953.jpg
    59 KB · Views: 26
The problem you will get is that because the switches will be in parallel, if either switch is on the light will be on, i.e if A turns it on, B will not be able to turn it off. Normal 2-way switching gives full control to both switches. Depending on whether a simple route exists between the two switches, it might be straightforward to pull in a new length of cable and configure it as a proper 2-way.

NB, before making any interconnection, it is essential to confirm that the two existing switches are on the same circuit. Most unlikely for them not to be, but interconnecting two circuits is dangerous and prohibited so it needs checking. I would connect both actives but insulate one neutral, otherwise the neutral will form a loop which would be confusing to anyone tracing it out in the future.
 

Reply to Connect 2 Separate Switches to Operate 1 Light in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock