Currently reading:
Earthing Arrangements Explained + Photo's

Discuss Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

Paul.M

-
Esteemed
Supporter
Reaction score
5,807
This is for the people still in or has just left their electrical education or for those of us that need a refresher in domestic earthing arrangements. It's all very well looking at prity diagrams in college and in books but its different when your out in the field for the first time. Hope this thread helps you and I hope that other members will post up their pictures of main incomers/earthing so others can learn and understand this subject better. I wish I could refer to something like this when I was in college.



First of all we have 3 types of earthing arrangements, TN-S, TN-C-S and TT.

TN-C-S
tncs1.jpg


This is where the main earth cable from the main earth terminal (met) is connected to the neutral at the suppliers main fuse. A good way to remember the name of this arrangement is to think of the C meaning COMBINED.


TN-S
image-3.jpg


This is where the main earth cable from the met is clamped or solderd to the steel of the SWA or the led outer sheath of the incoming supply cable. Again a good way to remember this is to think that the S stands for SHEATH.

TT
electrics_earthing_supply_types_and_bonding_meter_pos_tt-1.gif


The main earth cable from the met is connect to an earth electrode (aka earth rod). This is because not all properties are supplied with a TN system by the supplier so we have to insert a rod into the ground.


Notice how the earth cable on the TN systems go back to the main incomer, one goes to the main fuse (TN-C-S) and the other goes to the incoming cable (TN-S). If the main earth cable doesn't go back to the fuse or incoming cable it will be a TT. This is the simplest way I can put it without going into extended detail.



Now that we've seen some prity diagrams (am I starting to sound like a teacher lol) we will now look at real world photos that are not as straight forward as the diagrams.


First example, is it a TN-S or a TN-C-S or both?

IMAG0082-2.jpg
 
Last edited:
Thanks for this Paul. I haven't come across a TT system on-site yet, so great to see what it looks like in reality!!


Sorry meant to quote from the TT rod photo from post 59. Still it saves a bit of space.
 
Good points E54, I also wouldn't pig tail the earth cable. Wonder how long the connection will last exposed to the elements like that?

Just a note: Never pig tail a live conductor, you've basically just made an induction coil.
 
Hi all, since I'm only in my first year of my Level 2 C&G 2365 electrical installations it's always nice to be able to look at different set ups and recognise what they are, I saw the following and wanted to know if this one is a TN-C-S or TN-S install because I was thinking a TN-C-S but it looks like it's connected to the sheath so that makes it a TN-S install???

Thanks all
ImageUploadedByTapatalk1388086471.805616.jpg
 
Can't exactly see what type of clamp has been used in your photo, but if it's just a standard/typical pipe earth clamp, then it's not suitable for purpose, only Constant Pressure and Hepworth (think that's the name) clamps that require a tool to secure, are acceptable. 9 out of 10 TN-S cable sheath connections are made via soldered/lead wipe connections, clamps only being retrofitted as or when required!!
 
This is why I uploaded it, I came across the picture online and had an idea but since I'm a trainee was unsure, I certainly knew i had not seen it like that before, obviously I've seen a small percentage of what's to see but this was the 1st time I've seen some sort of clamp!!
 
Hi all, since I'm only in my first year of my Level 2 C&G 2365 electrical installations it's always nice to be able to look at different set ups and recognise what they are, I saw the following and wanted to know if this one is a TN-C-S or TN-S install because I was thinking a TN-C-S but it looks like it's connected to the sheath so that makes it a TN-S install???

Thanks all
View attachment 21921
if in doubt then do a Ze...and a Zpn....if the PFC is the same then you can be pretty certain that you have a TN-C-S....
if not then its likely to be TN-S...

TT should be obvious
 
On a TT system an earth electrode (aka earth rod) needs to be installed. The rod needs to be available for inspection and testing, this can be achieved by an earth pit as below.

Picture_1_-_Copper_Earth_Rod_Inside_Precast_Concrete_Chamber.jpg


Any thoughts on this?

Just looked back over this thread and should have mentioned that if a rod has an exothermic or brazed welded connection, it doesn't really need or warrant an earth pit enclosure, (but the rod to cable connection should still be protected, say with amalgamating tape) unless it's only for location identification purposes. I would imagine, that in this case it's one of more than one earth rod position, the first having a removable bolted clamp connection for testing purposes.

I'll assume that this rod is a part of an industrial or commercial earthing installation or maybe even a lightning protection system, rather from a domestic installation??
 
Just looked back over this thread and should have mentioned that if a rod has an exothermic or brazed welded connection, it doesn't really need or warrant an earth pit enclosure, (but the rod to cable connection should still be protected, say with amalgamating tape) unless it's only for location identification purposes. I would imagine, that in this case it's one of more than one earth rod position, the first having a removable bolted clamp connection for testing purposes.

I'll assume that this rod is a part of an industrial or commercial earthing installation or maybe even a lightning protection system, rather from a domestic installation??
like a nest....
 
Hi folks. New member but regular visitor. ThanELECTRICITY SUPPLY 011.jpgk you for this very interesting thread, in a nice style too. I'm hoping to resurrect it. What do you think of this one then? I'll have more pics to follow, but what does this say to you please?
 

Attachments

  • ELECTRICITY SUPPLY 011.jpg
    441.7 KB · Views: 217

Reply to Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock