Discuss EICR in Flat - cross-connected circuits, T&E tails, composite earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Just want to query this Dave. My understanding was that the earthing conductor for standard domestic PME was a minimum 10mm, based on the requirements for bonding conductors for PME installations, table 54.8. Is the 16mm necessary if adiabatic will allow 10mm?

You are probably right, but for some reason I have it stuck in my head that the earthing conductor needs to be 16mm with PME.
But it has been a good few years since I had anything to do with domestic and smaller supplies.
 
You are probably right, but for some reason I have it stuck in my head that the earthing conductor needs to be 16mm with PME.
But it has been a good few years since I had anything to do with domestic and smaller supplies.
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding gas, water, even cross bonding with 16mm.
 

Reply to EICR in Flat - cross-connected circuits, T&E tails, composite earth in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
499
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
721
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock