While it is possible to get a L-N fault that does not involve the CPC, it is hard to do with T&E cable due to its physical layout (CPC in the middle) and at accessories it is usually a fault to the back-box (cable nipped by screw sort of thing, missing grommet allowing cable-box cut, etc)

Do a continuity test L-N and see if it is low enough to trip the MCB side (so under 5-ish ohms) or it is tens of ohms or more like a small-medium motor waiting to start.
 
This is so confusing! You guys are so helpful.

Right, I have connected CPCs back to the earth bar in CU. Put both live and both neutral from the ring into a 5 way wago, with a new wire out from it to test. Put green lead from Megger on the CU earth bar and red onto the lead from the wago connecting ring together. Insulation resistance test on that gives 35.8 M Ohms.
 
Right, I have connected CPCs back to the earth bar in CU. Put both live and both neutral from the ring into a 5 way wago, with a new wire out from it to test. Put green lead from Megger on the CU earth bar and red onto the lead from the wago connecting ring together. Insulation resistance test on that gives 35.8 M Ohms.
That is good.

As a general rule, you always do IR testing with the CPCs connected to the MET (earth bar) so a fault to external metal / true Earth (e.g. screw through cable) is seen even if it is not touching the CPC conductors.
 
Right. Checking the pump is not so easy as the inspection hatch is a two man lift, as it is an inspection cover filled in with stone. However, I have reconnected the ring main back into the CU temporarily using Wagos and it has not tripped so far.
 

Reply to Fault on Ring final circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
702
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
944
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top