While it might not be exactly the same as your situation, here is a comparison of the break time versus current for a fuse (32A BS88 Gg type) in red, and a MCB (Schneider Acti9 iC60 32A B-curve) in blue. It shows at most overload currents the MCB is faster, most dramatically above the 100-150A region where the magnetic "instantaneous" trip takes over.

OK, will try later as it seems I can't upload the picture :(
Attached is the comparison, with my crude attempts to fill in the bits not plotted by the Schneider on-line tool.

Basically as current increases a fuse blow faster (though it gets complicated and a bit variable down below one-two cycles of the AC supply as the time being split in to pre-arcing when the element is still solid, and arcing when it has vaporised and the arc is dying down) whereas a MCB when it gets to the "instant" magnetic trip it operates in 5-10 milliseconds that decreases, but not massively, with higher fault current.

So in this case you see the 32A MCB (blue curve) has lower fault energy up to around the 0.5-1kA region (especially just above 100A when the magnetic trip fires) and beyond that the fuse (red curve) blows faster and is also far more effective at limiting the peak fault current / total let-through energy.

That is why it is still very common to see boards of breakers backed up by HRC fuses - the breakers have excellent behaviour at low/medium fault currents and can be reset quickly, whereas the fuses can sit there for decades and only blow under serious faults, but very quickly limit the energy so the breaker, busbars, etc, suffer much less risk of damage.
 

Attachments

  • MCB-fuse-32A-compare.jpg
    147.3 KB · Views: 24

Reply to Fuses replaced with higher amperage. Thoughts? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The breaker pictured trips with nothing plugged into the circuit. It is able to be reset and stays reset for several days, but trips again. When...
Replies
1
Views
516
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
499
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
338
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock