Currently reading:
Industrial lighting circuit

Discuss Industrial lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Jm1980

-
Reaction score
16
Hi guys

I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this.

Have done a few of these before and in the past i have sometimes run radials in SWA cable to single gang socket outlets. The High Bay LED lighting then connects via a normal 3 pin plug fitted with suitable fuse. Doing it like this has allowed individual fusing and easy disconnection of fittings (which was great in the early days when LED's seemed super unreliable).

Sockets were left non rcd but labelled, however being 12 metres up in the air nobody was likely to use them.

New job i have picked up is similar environment. Circuits will be swa wired, ref method clipped direct or on tray. The circuits will run on the metallic girders/structure in the roof however the lights will hang (jack chain) a good 3 metres below this. This is for 2 reasons, firstly the lighting design has indicated this height for the lux level required and secondly, the maintenance team at the site only has scissor lifts that will go so high (they will reach the hanging fittings but not the circuit wiring in the roof). Hence i need a way of extending my circuit down at each lighting point and a method of easy disconnection of fitting if possible.

I have seen similar done with a trailing socket outlet dropped down to lighting points via flex but this always seemed a bit rough to me as I've often seen 'not to be connected directly to the mains' on these sockets. Also now with the RCD requirements on socket outlets being tightened even further this would need a risk assessment to cover i presume? Doesn't seem worth the hassle.

Has anyone come across another way of being able to extend the circuit down for disconnection where the light hangs, preferably one that allows individual fusing? (although this is less of an issue now LED's seem a lot more reliable.)

Cheers

Jim
 
I have seen pc style trailing sockets used for this type of thing, they are small, rated for 10A load and easy to disconnect.
 
Wondering if a trailing Trucon 1 solution might work for you - I'll find a product link and post below but basically you could drop a flex lead down from the main run and use a trailing socket/joiner at a drop length that works to be able swap out and replace if needed. You wouldn't have that fused, but tbh I'm not sure the need is there anyway, and you'd have issues anyway guaranteeing that a 3-5A fuse would blow before the reaction time of an MCB/RCBO.
 
Do they need any specific IP rating?

These are cheap and for lighting (4 pole so PL/SL for emergency lights as well), but maybe an issue of cable types they would clamp:
https://www.NoLinkingToThis/p/greenbrook-20a-4-way-connector/176gv
 
Thanks for the replies guys.

No specific IP rating required, fittings and wiring all indoors.

I like the powercon connectors that Rockingit linked, will be having a look at those. Think the Greenbrook connectors might be an issue with the HO7RNF cable i had in mind for the drops down from the ceiling (and they look a bit flimsy/domestic).

Looking at it again i will probably split fittings up into a few more circuits than i planned so fusing at the fitting is less of a desire.

With the nature of the building and structure, the cabling really does need to be swa. Socket outlets have worked really well for me in the past but with no realistic access to the runs at ceiling height its not a sensible solution this time.

As im not using socket outlets this time how would others wire this circuit? All my calcs work out fine for 2.5mm swa 3 core with a c16 mcb. I need a method of terminating swa at each point so either a galv adaptable box or metalclad backbox with a 2.5mm flex glanded out and dropped down 3 metres to the connector and high bay?

Joints will be accessible if really needed (hire of a big enough scissor lift) but it would be a pain to have any issues with the circuit so how would others best connect the wiring inside the points, wago's would be allowed but what's others experiences of them long term? Current on each circuit will 6A approx

Thanks for the thoughts so far
 
As im not using socket outlets this time how would others wire this circuit? All my calcs work out fine for 2.5mm swa 3 core with a c16 mcb. I need a method of terminating swa at each point so either a galv adaptable box or metalclad backbox with a 2.5mm flex glanded out and dropped down 3 metres to the connector and high bay?

Joints will be accessible if really needed (hire of a big enough scissor lift) but it would be a pain to have any issues with the circuit so how would others best connect the wiring inside the points, wago's would be allowed but what's others experiences of them long term? Current on each circuit will 6A approx
I'd have some concerns about the risk of dirt/dust ingress up at that height but you could potentially use 3ch lighting track and just drop a flex outlet off as you need to. Would mean you could just run a 5c SWA up to the start of each length. Alternatively then I think you're stuck with an adaptable box or maybe a 20/25mm conduit 3way and wago's. Or, maybe just using conduit and singles (I'd imagine that they're all long straight runs so no need for many sets?) and take your SWA or HiTuff up to the start of each run, would save on all the glanding time. Only you know the environment and what you're looking at!
 
Many diffrent ways but one that springs to mind is M20 galv thru boxes woth dome plates to M20 stuffer? Or adaptable boxes with CPC links
circular_dome_cover_galvanised.jpg
 
Many diffrent ways but one that springs to mind is M20 galv thru boxes woth dome plates to M20 stuffer? Or adaptable boxes with CPC links
View attachment 111860
Yes, that's basically where I was at only using a 3way instead of the added expense of the dome top - also one less cpc to do.
 
Thanks for the input guys.

Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped direct looks by far the easiest way of doing it. Had another look today and i like the galv adaptable boxs with a stuffing gland out for the flex drop.

The 2 way through box and dome top would make the job a little quicker i think but there's something that i think looks ugly about swa into a through box (not that anyone will see it 50ft in the air!)..........i also think with 2 x 2.5 cables and the flex, the through box might start to get a little cramped.

Regarding my question of wago's used at junction points/adaptable boxes............would anyone have any reservations about using? Ive yet to see any joints with wago's that have 'gone bad' but wondered what others thought?

Cheers

Jim
 

Reply to Industrial lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock