I opened up a LED lamp that measured leaking AC voltage 70 Vac and sometimes after on is 78 Vac or so. The volt is stable AC and DC no reading.
I have checked with LED lights ON, the leakage is not from the driver, connectors,.... I isolated all drivers, connectors,.... away from frame to determine no AC leak but only LED strip that is glued to the frame. So last result LED strip leaked this AC voltage.

LED Driver Specification: 2 wires, AC 240 Vac 0.33A to 2 wires 24-40 Vdc, max 36W, max 900mA SELV.
LED connection: 5 LED in series, Total LED 120, type 5050 LED.
Measurements:
Driver output NO LOAD: 104Vdc
Driver output LED all ON: 72.8Vdc, 160mA
Ground to LED Strip Negative: 30M ohm
Ground to LED Strip Positive: 40M ohm.

Question:
Why is leaking AC, not DC?
What is SELV?
 
what do you mean by leaking?
a voltage is a potential difference between 2 or more points ,presence of a voltage ac or dc means little ,its the current that flows or could flow thats important.
its usually a capacitor or other component for emi that causes these things , if from a reputable manufacturer all should be ok.
 
what do you mean by leaking?
a voltage is a potential difference between 2 or more points ,presence of a voltage ac or dc means little ,its the current that flows or could flow thats important.
its usually a capacitor or other component for emi that causes these things , if from a reputable manufacturer all should be ok.
Leaking means measure from ground of frame to AC ground. There is no capacitor and no resistor.
Its dangerous to have such high leakage.
 

Reply to LED Strip leaking AC reading. in the Lighting Forum area at ElectriciansForums.net

Similar Threads

I am currently looking to add 12v led cob strip lights to my mother's kitchen but confused what I need. There are currently mains wires under the...
Replies
2
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top