Search the forum,

Discuss New house supply from 3 phase next door in the UK Electrical Forum area at ElectriciansForums.net

M

miner69er

Hi Everyone, i'm after some input...
New house been built and i need to install a mains cable from 100Amp 3 phase in unit next door (unit is part of the plot and just oversized garage)
Now.... i've never installed bigger than 6mm square for outbuildings etc. House is to be single phase only. Looking at the big green book, 25mm SWA 3 core should suffice with the cable being buried at the correct depth. But should i bury it in conduit or lay direct in the ground. And any other advice on the subject of laying the mains would be greatly appreciated.
 
Hi Everyone, i'm after some input...
New house been built and i need to install a mains cable from 100Amp 3 phase in unit next door (unit is part of the plot and just oversized garage)
Now.... i've never installed bigger than 6mm square for outbuildings etc. House is to be single phase only. Looking at the big green book, 25mm SWA 3 core should suffice with the cable being buried at the correct depth. But should i bury it in conduit or lay direct in the ground. And any other advice on the subject of laying the mains would be greatly appreciated.

Gasp!!
 
I would be more worried about where you are going to connect it!
You should really speak with the DNO and get a seperate meter put in there.
 
okay guys. yes i didn't word that the best way i could have. i just wondered if there was going to be any benefit in laying the cable in conduit between buildings rather than direct in the ground which, by the way i have always done going to outbuildings etc.
The meter is already in the unit ready to be connected to, from whatever was originally connected to it.
 

Reply to New house supply from 3 phase next door in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
1K
What are peoples opinion's on this, pair of big old semi-detached houses (85 and 87) converted into apartments, dont think its a HMO although it...
Replies
1
Views
284
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top