Search the forum,

Discuss Potential boiler issue in the UK Electrical Forum area at ElectriciansForums.net

JP0704

DIY
Reaction score
5
Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP!

Every so often (twice in the last two days) when running the hot water in the kitchen it trips our electrics (downstairs lights, sockets, cooker and boiler) and cannot be reset for a good 20-30 mins. This only happens randomly and when running the hot water. We have unplugged all appliances except cooker and it still happened. We have had an electrician out who said all is good (EICR done in July 2023 and all good) and had plumber out to service boiler and also run through cycles of high fire and low fire with no issues (this was completed during the daytime,
Not evening).
We have had the water pressure sensor changed but no change to trips.
When having a shower in the evening it has not tripped the electrics, it only seems to be when using the kitchen hot water.
Any advice greatly appreciated.
Thanks
Jon
 
There will be certain things like valves and pumps that only switch in when the boiler is running…. A general insulation resistance test with power off may not find these problems.

Is the upstairs and downstairs on separate hot water pipes… maybe one is through a motorised valve?
The valves can be manually held open with power off for IR testing.

If it’s only happening sometimes and not always… it could be difficult to find a fault.
 
Sorry for the not helpful reply but I am not sure how I would find out if downstairs is on different pipes to upstairs.
Would changing of the boiler / electrical board solve the issue or is it likely to be an individual motorised valve?

What/who would you recommend I ask to try solve the riddle?
It sounds like an expensive fault to find…
 
I would be looking carefully for any water leaks near the kitchen sink.
 
I would be looking carefully for any water leaks near the kitchen sink.
Hi James.
Thanks for your reply. We recently had the condensate pipe from the boiler replaced as it was leaking into the cupboard below the sink. There is a socket under there which connects the dishwasher but doesn’t explain why the trips are so random?
 
Hi James.
Thanks for your reply. We recently had the condensate pipe from the boiler replaced as it was leaking into the cupboard below the sink. There is a socket under there which connects the dishwasher but doesn’t explain why the trips are so random?
Is there any evidence of a leak from the kitchen waste pipe under the sink, eg joints, trap or appliance waste connections, or a leak from around the sink etc? Can you turn off power to the socket under the sink at the consumer unit, and if so does that make any difference (eg if you leave it off 'permanently'?)
 
Is there any evidence of a leak from the kitchen waste pipe under the sink, eg joints, trap or appliance waste connections, or a leak from around the sink etc? Can you turn off power to the socket under the sink at the consumer unit, and if so does that make any difference (eg if you leave it off 'permanently'?)
Hi. Thanks for the reply. No evidence in terms of water dripping / wet to the touch or signs of a leak on any other pipes.
I don’t believe that can be isolated separately but can check.
The plumber we had round for a separate issue said could be the PCB board?
 
So the fault only occurs when the kitchen hot tap is used, the fault doesn't occur when other hot taps are used, the fault clears itself after 20/30 minutes?

It could be that the hot pipe to the kitchen tap is very close to a damaged cable or other part of the electrical installation and when it gets hot the expansion puts pressure on it causing the tripping.
 
The plumber we had round for a separate issue said could be the PCB board?

If it was a problem with the boiler you would expect it to happen with all hot water taps, not just the kitchen.

If the fault only occurs when the kitchen tap is used then the cause is most likely to be something which is unique to the kitchen tap.
The boiler and it's associated systems are going to be common to all of the hot water outlets.
 
If it was a problem with the boiler you would expect it to happen with all hot water taps, not just the kitchen.

If the fault only occurs when the kitchen tap is used then the cause is most likely to be something which is unique to the kitchen tap.
The boiler and it's associated systems are going to be common to all of the hot water outlets.
Thanks Dave.
Yes it has only been related to the kitchen tap thus far and only has ever tripped in the evening time when washing up dinner plates. Has not happened during the day when using the kitchen tap (as mentioned above the boiler has been checked twice running through various cycles- high / low fire etc and didn’t trip)
So question is should we seek to find an electrician or a plumber to look at it?
 

Reply to Potential boiler issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good Afternoon All, I moved into a flat around 2 months ago. A few times only (maybe four times in the two months) I've turned on the kitchen...
Replies
14
Views
1K
Hello, I added a 240v insta hot water heater at the kitchen sink. When the water heater is in use the lights in the adjacent dining room flicker...
Replies
1
Views
832
So I’ve been having this issue with my boiler for a while now, I’ve currently got one stat in the hall that when I turn it on it brings the...
Replies
4
Views
721
A house we have just re-wired has one of these cooker points, Trouble is the kitchen wasn't supposed to have been touched by any trade but...
Replies
6
Views
331

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock