Is fault protection maintained with a type C or D. If you have no rcd protection in place a type D is a bad idea as they are not suitable for the protection of general socket outlets.
What make is the consumer unit.
 
Do you have the manufacturers information to calculate what curve MCB is required?

Also is the Zs of the final circuit sufficiently low for a type C or D.

Also a type D isn't really suitable for domestic socket outlets, I would consider running in a sperparte circuit if a type D is required.

Much easier to buy a food processor at the correct voltage and frequency rating, there's quite a large selection available...
 
Type D are rare as few loads need them, and for higher current type D MCBs it can be hard to meet the 0.4s disconnection time for final circuits (you need quite a low Zs to hit the magnetic trip to meet that specification).

They tend to be for protecting sub-mains (when 5s on the thermal part is OK), but are not as good as fuses there in terms of selectivity with downs stream MCB/RCBO. Or for high inrush things like big transformers and motors, again not a common domestic type of load.

Also if you are regularly switching a load that needs a type D MCB due to inrush you will find you switch has a short life...
 
Good pointers people am will look into type c mcb, to be honest have not taken tranny to friends house yet might not even trip, just tested at his home
 
Type D are rare as few loads need them, and for higher current type D MCBs it can be hard to meet the 0.4s disconnection time for final circuits (you need quite a low Zs to hit the magnetic trip to meet that specification).

They tend to be for protecting sub-mains (when 5s on the thermal part is OK), but are not as good as fuses there in terms of selectivity with downs stream MCB/RCBO. Or for high inrush things like big transformers and motors, again not a common domestic type of load.

Also if you are regularly switching a load that needs a type D MCB due to inrush you will find you switch has a

Good pointers people am will look into type c mcb, to be honest have not taken tranny to friends house yet might not even trip, just tested at his home
Schneider produce d type breakers 1 pole up to 60A din rail mount.
I have one of these
 

Reply to transformer tripping mcb in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Hi guys, I’ve just looked in my consumer unit and I’ve got space for an extra MCB and a rail transformer for my ring doorbell. I’m planning on...
Replies
1
Views
4K
Hi, does anybody know what other brands of MCB (if any) will fit an axiom consumer unit? I need a C32 breaker but i cannot source axiom C curve...
Replies
25
Views
7K
Hi, The RCD which protects my 16A ring main always "trips" when I plug/unplug a Laptop power supply. No other type of appliance causes a problem...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top