There's conflicting information going on here. Outspoken info understand what your saying and just because at the start of the circuit is the max VD as it has the most load upon it. Doesn't mean it's not going to drop more by the time it reaches furthest point and got operation of things working, that's what im interested in. So an accumulation of volts dropped by the time it reaches last point. Which is surely what the regs require us to obtain.

Monkey, FFS, the calculation of the TOTAL voltage drop across the entire circuit tells you the voltage at the END of the circuit FFS....

If the Volt drop is calculated at 4V (Thus dropping to 226V) the the voltage at the end of the circuit is ...Yep, you guessed it 226V ...it is not Rocket Science!
 
i'm bowing out before i suggest that you got 10V to play with anyway as we have 240V at source, but calculate VD from 230V. courtesy of the meddling euro rats in brussels.
 
I'm not stupid and I do get what you are saying. I know how to calculate the entire load of a circuit then use VD calcs to obtain total VD. I was always taught that you had to work out each leg individually. As the way your explaining it is assuming the total load is at the end of the circuit rather than it branching off at various points. Do you not see my point. But I will go with everything you say as you clearly have worlds more knowledge/experience. And if in your examples is correct way to
Determine total VD for a branch circuit, then I will leave it as that. As its a simpler way to calculate.
 
I had considered pointing out that if you measure voltages in the UK the averages for single and three phase are 236.7V and 415.8V respectively...but realised he was confused enough as it is!! :)
 
I'm not stupid and I do get what you are saying. I know how to calculate the entire load of a circuit then use VD calcs to obtain total VD. I was always taught that you had to work out each leg individually. As the way your explaining it is assuming the total load is at the end of the circuit rather than it branching off at various points. Do you not see my point. But I will go with everything you say as you clearly have worlds more knowledge/experience. And if in your examples is correct way to
Determine total VD for a branch circuit, then I will leave it as that. As its a simpler way to calculate.

Monkey, FFS, whoever taught you that is a frigging idiot as you will always end up with incorrect figures, that is why i gave you the example I did, to PROVE you MUST calculate the total maximum demand on the maximum length of the circuit to establish the true maximum volt drop you may experience. Obviously in the example I gave this will be variable as lights are turned on and off on various branches, thus you need to calculate the worst case scenario, if this is within the permitted levels with BS7671 then everything else is a pointless waste of your time!
 
Haha this could of been over a lot earlier if I'd seen this sentence at the beginning.

you MUST calculate the total maximum demand on the maximum length of the circuit to establish the true maximum vd
 
Monkey, FFS, the calculation of the TOTAL voltage drop across the entire circuit tells you the voltage at the END of the circuit FFS....

If the Volt drop is calculated at 4V (Thus dropping to 226V) the the voltage at the end of the circuit is ...Yep, you guessed it 226V ...it is not Rocket Science!

Well put and better than a thousand diagrams :)
 

Reply to Volt drop cont. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
995
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
680
I am working on a RV Park and I have a question. I plan on installing 4/0 quadraplex AL URD cable to 10 pedestals on a 200 amp circuit and...
Replies
0
Views
243
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top