3 Phase converter.

Discuss 3 Phase converter. in the Commercial Electrical Advice area at ElectriciansForums.net

S

screech

Hey guys.

My mate is looking at a new compressor for his body shop.

The only thing is, its 3 phase and he only has single phase in the workshop.


Has anyone had any experience with any 3 phase converters? Obviously this would be cheaper than having UKPN come to put a 3 phase supply in.

I'd imagine theres a lot out there, but what one are good, if any, and what ones are not?

The compressor is a 10hp motor!


Any advice would be appreciated.


Cheers
 
My mate needs to buy a new filling machine. The local water mains can only supply 10 litres a second but he needs 30 litres a second. Does he buy a filler than can keep within the limits of the mains or get a machine that can't?

.
 
I'm going to pretend there's only been 2 replies.
Thanks for the useful comments.

I've had a little look into it and can see its going to be an expensive bit of kit.
Would like to know if anyone has had any experience with them.

Cheers
 
Silva is making a very good point albeit using plumbing terms .... converting 1ph to 3ph will have a triple duty approx. on single phase to the rating of the 3ph motor.... you say its a workshop which is only single phase so can the supply handle it and is he ready for the electric bill??? short term it might be cheaper to do this way long term may be cost effective to have 3ph brought in.
 
Thanks, I do see your point. I'm asking as that's what he's asked me to do.
I've not looked much into the converters yet so no idea what sort of supply they need.
The workshop currently has 100a single phase.

I know he's been offered this compressor for a good price, plus I don't think they are available in this size in single phase.

I'm going to call the board tomorrow to get a quote and see what they want.

Cheers
 
100A single phase

Get your mate to ask about getting a 3 phase supply as I have a horrible feeling he is going to add more equipment in the future and that won't be big enough.
 
Hey guys.

My mate is looking at a new compressor for his body shop.

The only thing is, its 3 phase and he only has single phase in the workshop.


Has anyone had any experience with any 3 phase converters? Obviously this would be cheaper than having UKPN come to put a 3 phase supply in.

I'd imagine theres a lot out there, but what one are good, if any, and what ones are not?

The compressor is a 10hp motor!


Any advice would be appreciated.


Cheers

Hi Screech,


I don't know much about 3 phase converters, but i can give advice on different types of compressors like air, screw, compressors where we ordered. want approach them.
 
I don't think it's as big a problem as people are making out. He could use an invertor connected to just the compressor. Am I right in saying 10HP is around 7.5kW? A single phase input invertor would be around £600 I would guess.

Single 230v phase input/3 phase 230v output connected to the compressor. So it would have to be able to be connected in delta. A little design of the run signal and it should be OK.

Only issue is the 8kW or so input, around 30 odd amp. It would be like having an 8kW shower running all the time. Obviously it will knock off when the required pressure has been reached.

So a little unconventional but certainly do-able, unless I am missing something.
 
I don't think it's as big a problem as people are making out. He could use an invertor connected to just the compressor. Am I right in saying 10HP is around 7.5kW? A single phase input invertor would be around £600 I would guess.

Single 230v phase input/3 phase 230v output connected to the compressor. So it would have to be able to be connected in delta. A little design of the run signal and it should be OK.

Only issue is the 8kW or so input, around 30 odd amp. It would be like having an 8kW shower running all the time. Obviously it will knock off when the required pressure has been reached.

So a little unconventional but certainly do-able, unless I am missing something.
As ive already mentioned and yes your missing something... you convert 1ph to 3ph you triple the demand on the supply now its highly likely he has a 3ph 400v motor and you can get inverters 230v 1ph to 400v 3ph but these again add to the load in comparison to 1ph 230v to 3ph 230v.... this compressor could be taking around 40% to 70% of the supply and duty of the compressor all comes down to what he is attaching to it and given the size of it he has a few heavy pneumatic loads.
 
As ive already mentioned and yes your missing something... you convert 1ph to 3ph you triple the demand on the supply now its highly likely he has a 3ph 400v motor and you can get inverters 230v 1ph to 400v 3ph but these again add to the load in comparison to 1ph 230v to 3ph 230v.... this compressor could be taking around 40% to 70% of the supply and duty of the compressor all comes down to what he is attaching to it and given the size of it he has a few heavy pneumatic loads.

Not sure I follow. What do you mean triple the demand on the supply?

Plus I think the point made is that the compressor motor would need re-linking from star to delta configuration to convert it from 400V 3ph to 230V 3ph.

What am I missing?
 
If you say have a 1ph fixed load of 10 amps it will draw 10amps off the supply, now say you have a 3ph load whether you can use 230v or 400v motor connections and you want to fit an inverter to allow it to run off 1ph then the 1ph supply has to provide power for the electronically generated 3ph all of which will take 10amps per phase in this example so the duty of the motor on the mains would be triple the plate rating .... this would increase if you try to use an inverter that also has to increase the voltage too 230v - 1p in / 400v - 3ph out.
You can't get something for nothing if the inverters were 10amps in 1ph and 10amps out 3ph then they would be called perpetual machines generating 66% more energy out than put in.
 
Not sure I follow. What do you mean triple the demand on the supply?

Plus I think the point made is that the compressor motor would need re-linking from star to delta configuration to convert it from 400V 3ph to 230V 3ph.

What am I missing?

You are suggesting a motor inverter. The largest off-the-shelf one I could find was 2.2kw. Please link us to a 7.5kw one you know of. Or regurgitated manuf. spec of input supply requirements.

.
 
Example ..I have here in my hand a 4kw Omron inverter 1ph to 3ph now given that a 4kw motor will have an flc of approx. 8amps the plate rating gives a input demand of 40amps so do the maths that is 5 times the motor flc rating because you generate it from a single phase supply .... now take the OP example 7.5 KW motor and do the same.... with approx' 14amps flc x 5 this could see a demand of up to 70amps on the 1ph supply of which has a cutout fuse carrier stamped 100amps although this may not be the fuse rating within. As silva has pointed out once motors start getting beyond 4kw the duty on a single phase supply becomes so large it not commercially viable to make a product that would see little demand although you can get them they aint cheap .. don't mix this up with 3ph in 3ph out inverters which come in all size as ive just fitted a 33kw inverter myself.
 
Last edited:
You are suggesting a motor inverter. The largest off-the-shelf one I could find was 2.2kw. Please link us to a 7.5kw one you know of. Or regurgitated manuf. spec of input supply requirements.

.

See my post, No.2. link to 10hp 1 to 3 ph.

From spec "At FULL LOAD this unit would require a 220 Volts feed of 50 Amps",
 
Example ..I have here in my hand a 4kw Omron inverter 1ph to 3ph now given that a 4kw motor will have an flc of approx. 8amps the plate rating gives a input demand of 40amps so do the maths that is 5 times the motor flc rating because you generate it from a single phase supply .... now take the OP example 7.5 KW motor and do the same.... with approx' 14amps flc x 5 this could see a demand of up to 70amps on the 1ph supply of which has a cutout fuse carrier stamped 100amps although this may not be the fuse rating within. As silva has pointed out once motors start getting beyond 4kw the duty on a single phase supply becomes so large it not commercially viable to make a product that would see little demand although you can get them they aint cheap .. don't mix this up with 3ph in 3ph out inverters which come in all size as ive just fitted a 33kw inverter myself.

Ok, I think you might have to educate me.
Keeping it simple and only looking at power in vs power out.

Are you saying the plate rating of the 4kW inverter is 40A at 230V? That would be 9.2kW.
I am finding it hard that if it is giving 4kW out it is taking 9.2kW or only 43% efficient - that is pretty damn inefficient whatever the technology it has inside and it must get pretty hot!

snowheads spec sounds better to me. 220V at 50A is 11kW. 10hp being 7.5kW. So 68% efficient assuming

What is wrong with my logic?

I should add that I have limited experience of inverters but I do have a 1.5hp one on my lathe. Its manual quotes 230V @ 12A in vs 230V at 6A out. Given that is 6A per phase I make that 2760W in vs very roughly 2400W out if I have done my sums right.
 
Sorry but I still can't see what the problem is. He has a 10HP (7.5kW) 3 phase motor that he needs to supply. If he uses a 230v single phase in/230v 3 phase out invertor, he would have to connect the motor in delta to accept this 230v.

If the invertor was 100% efficient it would be 7.5kW in/7.5kW out. As we know it will not be that efficient so you could expect to have to put in more than you take out. The input is unlikely to be treble the output because each phase is 120 degrees apart will be closer to 1 over root 3 (1.732).

Forget about using the motor in star for 400v operation as it is perfectly capable of working at 230v in star. To get a 230v single phase in/ 400v 3 phase out would be unecessarily expensive.

These are widely used in industry, and Routeco have them for example.
 
Sorry but I still can't see what the problem is.

These are widely used in industry, and Routeco have them for example.

Firstly, interpretations of converter are being crossed here, I think. I believe the OP was inquiring about supply converters rather than motor inverters.

Secondly, please link to a single phase 7.5kw inverter drive on Routeco as I can't locate, but this phone is awkward for browsing.

.
 

Reply to 3 Phase converter. in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock