Have you verified that there isn't an erroneous connection to another circuit?
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.


OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.
 
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.


OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.
Apologies. I read it that there was a cable connected to it, but that it was no longer used.
 
Thanks, yes, I have tested all breakers. That's how I found this one. I did the full range of tests, including ramp tests etc and recorded all values, before the electrician who will issue the certs comes and does his own. I installed a full RCBO board in my new kitchen (which is the main test job) and this board was previously installed in another space to serve other circuits. It was the only faulty MCB.

For the record, I looked into trading standards in Kent. They hive reports straight off to Citizens Advice. They in turn made it clear that they are not the slightest bit interested in this, and nor would trading standards be either, unless I could identify a criminal individual or organisation.

Hager has no complaints facility on line. Surprising. When I rang customer services, it took some time to explain the problem as the operator in customer services had no idea what an MCB was. It was suggested that I contact the seller. When I suggested in turn that it may be counterfeit or faulty goods, they suggested I return the item to them if I wanted to, at my cost. So that is a no then!

An MTN140 Type B 6kA costs £3.99 with free prime delivery (same or next day) from Amazon. Only £2.46 at Edwardes. It is simply not worth messing around with. In this case I do not believe that the item was counterfeit. It is just faulty, and if they can make them that cheaply (retail must be double ex factory cost) then it is inevitable that some will be defective.

Interesting experience though.
 

Reply to 40 amp MCB live when off? Faulty? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock