Only one answer to this. Carry out the full design process to determine the answer.

Just remember.

9.5 KW = 41A so the protective device must be 45A or 50A depending on CU. take into account the following down rating factors for starters.
Grouping factors
Insulation
Installation method.

6mm has never been big enough for 9.5 KW so can not be classed as does not comply with current regulations.
If it trips regularly there is an issue that must be addressed. The fact that it is only used for a short time is not the correct approach.
This is a C2 fault potentially dangerous.
 

Reply to 9.5 kw shower on 6mm ? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock