Search the forum,

Discuss A few things I have been wondering about in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

L

LeonardS

from what I understand when live is down to earth there is less resistance then taking the intended path through the return conductor to earth at the head or in the road depending on supply system, so more current is drawn as voltage wont change unless its stepped down or up, but will vary in a AC circuit. so a MCB would trip because of overcurrent. I am wondering why doesnt a mcb trip when you touch a live conductor and you're not electrically common as there is even less resistance to earth hence why you're not electrically common? or why the RCD doesnt trip as there would be a load imbalance?
 
human body is arround 1kΩ resistance, hence using ohm's law, I=V/R, I = 230/1000 = 0.23A which will not trip MCB but may kill you.
 
Last edited:
Thanks for clearing that up, I had answers from the sparks claiming its not making contact with circuit earth, which didn't make sense to me as neither does a MCB haha,

few other things, I was fault finding with a sparks the other day and the lights where not coming on, we found it was because of a loose neutral connection the voltage displayed was much less then 230V but greater then 0V I'm curious why we picked up voltage as theres no path to earth

second thing is why do you have voltage on a ring circuit with no load for the same reason no path to earth it must be the voltage indicator is making that connection? in which case there must be a resistor in a voltage indicator as the mcb would trip?
 
Thanks for clearing that up, I had answers from the sparks claiming its not making contact with circuit earth, which didn't make sense to me as neither does a MCB haha,

few other things, I was fault finding with a sparks the other day and the lights where not coming on, we found it was because of a loose neutral connection the voltage displayed was much less then 230V but greater then 0V I'm curious why we picked up voltage as theres no path to earth

second thing is why do you have voltage on a ring circuit with no load for the same reason no path to earth it must be the voltage indicator is making that connection? in which case there must be a resistor in a voltage indicator as the mcb would trip?

It must be me Leonard, I can't make head nor tail of what you are asking.
 
if you think of an analogue voltmeter, it requires a specific current to move the needle. the more current, the more the needle moves. now, it only requires a few millivolts to do this, so there will be circuitry in series with the meter movement to drop the bulk of the voltage across it. say for arguments sake, the meter movement reqires 1mA for fsd. then the resistance in series will be as near as dammit 230/0.001 or 230kΩ.
 
and the voltage I was getting when the neutral was loose on the lighting circuit? I was getting below 230v an above 0v why was that? no path to earth so no voltage should of been picked up?! I believe I was getting like 12v between live and neutral
 
With a loose Neutral, rather than a disconnected Neutral, you would have a high resistance connection.
I believe there is an equation you can use which would enable you to determine just how much resistance the connection had using the supply voltage and the measured voltage.
 
human body is arround 1kΩ resistance, hence using ohm's law, I=V/R, I = 230/1000 = 0.23A which will not trip MCB but may kill you.

Slightly off topic but this reminds me of a lunch time when were meggering KFC Chicken Wings , Tower Burgers, Hash Browns etc. It was so funny but interesting at the same time!! Chicken Wings (all that grease) have quite a low IR lol
 
human body is arround 1kΩ resistance, hence using ohm's law, I=V/R, I = 230/1000 = 0.23A which will not trip MCB but may kill you.

Not everyones is 1kΩ. The best way to test this is get an apprentice, give him the megger probes so you can measure his resistance, crank it up to 1000 and tell him everything will be fine its all in the name of science.....

zap.
 
Not everyones is 1kΩ. The best way to test this is get an apprentice, give him the megger probes so you can measure his resistance, crank it up to 1000 and tell him everything will be fine its all in the name of science.....

zap.
but will the bugger keep still long enough for you to get a reading on the meter?
 
years ago, a regular client's brat was always rooting in my toolbox. i put a couple of charged caps in. soon stopped the little bugger.
 
I do not advocate the electrocution of minors,of course....but i find if you paint your large,capacitors orange,and write "dynamite" on their side,the little rascals seem drawn to them...:bobby:
 

Reply to A few things I have been wondering about in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top