Afternoon all, Just looking for opinions. Basically the other day I was sent to do a defects report on a building we designed the electrical installations for. So there was no testing as the contractor did this, I just had to make sure everything worked, Looked good etc.
It's the second time I've done one of these recently and on both occasions came up against the same two problems.
1) Labelling of FCU's etc, On both occasions circuit numbers and the use for the FCU had been labelled in marker pen, Not a proper label....I know there is nothing wrong with this, But it looks naff, Surely I aren't the only one who would pull this up?
2) Emergency test keyswitches, Again I was under the impression these needed to be engraved 'EM LT TEST' or something similar. But after seeing it on both sites I'm beginning to think I'm wrong?

Am I being harsh? Or have I just picked two bad examples in otherwise good work?
 
Afternoon all, Just looking for opinions. Basically the other day I was sent to do a defects report on a building we designed the electrical installations for. So there was no testing as the contractor did this, I just had to make sure everything worked, Looked good etc.
It's the second time I've done one of these recently and on both occasions came up against the same two problems.
1) Labelling of FCU's etc, On both occasions circuit numbers and the use for the FCU had been labelled in marker pen, Not a proper label....I know there is nothing wrong with this, But it looks naff, Surely I aren't the only one who would pull this up?
2) Emergency test keyswitches, Again I was under the impression these needed to be engraved 'EM LT TEST' or something similar. But after seeing it on both sites I'm beginning to think I'm wrong?

Am I being harsh? Or have I just picked two bad examples in otherwise good work?


If the contractor has done a cowboy job, then pull him up about, your comment no testing worries me a bit though.
 
What does it say in the design specification which you are using as your point of reference for this inspection?
If it specifies that labelling must be of a certain size, typeface and contain specific information then they are in the wrong, if it just says that accessories must be labelled then although rough you probably don't have much of a case.
The same with the test switches, what does the specification say?


Sent from my iPad using Tapatalk
 
What does it say in the design specification which you are using as your point of reference for this inspection?
If it specifies that labelling must be of a certain size, typeface and contain specific information then they are in the wrong, if it just says that accessories must be labelled then although rough you probably don't have much of a case.
The same with the test switches, what does the specification say?

Sent from my iPad using Tapatalk

Though I didn't actually spec the job I'm sure it says about labelling of emergency test switches, Though I don't think there is any specific indications as to what labels to use. I'm just thinking back to when I was on the tools, If id have labelled a spur or switch up with marker pen I'd have been labelled up myself, With offensive words!...
 
Though I didn't actually spec the job I'm sure it says about labelling of emergency test switches, Though I don't think there is any specific indications as to what labels to use. I'm just thinking back to when I was on the tools, If id have labelled a spur or switch up with marker pen I'd have been labelled up myself, With offensive words!...

Do you not have copy of the spec to use when carrying out the inspection?
 
Writing on an FCU with a marker pen is rough in my opinion. You can get a label printer for next to nothing. Even permanent marker will start to wear off after a few wipes with a damp cloth. Daz
 
I wouldn't say you are being harsh with the marker pens. As DPG said, after a few cleans, you wont be able to see it... and a label would make the job look more "professional" - like the contractors had some pride. & with the EM test switches, it makes it easier to locate and a much neater job
 
I don't think there's anything "wrong" with either of the points you've mentioned, unless you had specified otherwise. From a regs point of view there's nothing to say you can't mark up a FCU with a marker pen instead of a printed label, or even marked up at all as long as it's clear what it does. I don't think you even need a keyswitch at all - you could test the emergency lights by turning off the breaker provided that will leave adequate light so as not to impede safety.
That said I wouldn't feel comfortable doing that - I like to take pride in my work. Were the contractors chosen because they offered to do the job the cheapest?
 
I don't think you even need a keyswitch at all - you could test the emergency lights by turning off the breaker provided that will leave adequate light so as not to impede safety.
I don't agree.

8.3.3 Test facility

Each emergency lighting system should have suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply).
NOTE An automatic test system for battery powered emergency lighting is specified in BS EN 62034.


(Source: BS 5266-1:2011 incorporating Corrigendum No. 1)
 
I don't agree.

8.3.3 Test facility

Each emergency lighting system should have suitable means for simulating failure of the normal supply for test purposes (i.e. without interruption of the normal supply).
NOTE An automatic test system for battery powered emergency lighting is specified in BS EN 62034.


(Source: BS 5266-1:2011 incorporating Corrigendum No. 1)
Have you ever seen a system where switching the keyswitch cuts the supply so the lights go off and the emergency lights come on so you can see at a glance what's working and what's not? Depending on how the circuits are divided up the keyswitch has the same effect as turning the breaker off.
It's a perfect system for an office block where testing is done out of hours or when and where there is sufficient natural light not to cause a problem. Not suitable for internal corridors which would be plunged into darkness though.
 
Have you ever seen a system where switching the keyswitch cuts the supply so the lights go off and the emergency lights come on so you can see at a glance what's working and what's not?

Of course, but such a setup is contrary to the requirements of BS 5266-1:2011 as I have demonstrated and therefore should not be installed that way.
 
That's the way you've interpreted it.
To me that regulation contradicts itself - how do you simulate failure of the normal supply without interrupting it?

It's not contradictory. You are simulating failure of the normal supply to the emergency luminaires without interrupting the normal supply. This is achieved by interrupting the permanent line to the emergency luminaires.

I can safely state that it isn't just my interpretation - it is the intent of 8.3.3.

It is a common defect for key switches to be installed the way you have outlined - but it is a defect nonetheless.
 
Having done the FIA / ICEL course on emergency lighting only the other week we were told that it is exactly as Risteard has said.
The test switch should only interrupt the supply to the emergency lights, not the whole circuit


Sent from my iPad using Tapatalk
 
My understanding is also that BS5266 requires the test switch to only operate the emergency lighting, and not switch off the normal lighting.
Unfortunately doing such is not satisfactory for a couple of reasons.
With many maintained lights, there will be no indication that the em light is operating other than the charging indicator lamp will go out.
Another problem is that there is no indication whether lux levels are sufficient.
Lux levels can be altered by alterations to the fabric of the building, deterioration of lamps, accumulation of dirt and grime or even a change in decor.
To my mind it is ludicrous to require a testing system which will not even indicate that the em lights are working, or allow an assessment of lux levels.
 
Last edited by a moderator:
I must admit I always thought it was in the Regs for emergency Keyswitches to be marked up as such, But I've had a quick scan through and cant find it so I assume I am wrong and that it's just good practice.
I've wired emergency lighting systems In both ways stated, And IMO it makes more sense for an emergency keyswitch to override the normal lighting circuit as well, I can however also see that from a safety point of view It's better just to test the emergency circuit. I believe I asked the same question on another post, and was told That emergency switches should only isolate the emergency circuit as Risteard has said.
 
Unfortunately doing such is not satisfactory for a couple of reasons.
With many maintained lights, there will be no indication that the em light is operating other than the charging indicator lamp will go out.
Another problem is that there is no indication whether lux levels are sufficient.
Lux levels can be altered by alterations to the fabric of the building, deterioration of lamps, accumulation of dirt and grime or even a change in decor.
To my mind it is ludicrous to require a testing system which will not even indicate that the em lights are working, or allow an assessment of lux levels.

To be fair if the charge indicator ceases to illuminate (but illuminates when the supply is restored) then it would seem reasonable to assume that an emergency luminaire had been running off the battery during test.

As for lux levels etc. these do not need to be determined during the monthly test etc. If you wanted to determine them at another time this could easily be achieved by isolating all of the lighting in the area when it is dark (and when the building is not in use of course). That doesn't mean that the test switch isn't suitable for ensuring the emergency luminaires are operating on failure of the supply.

It should also be remembered if running a full duration test that the batteries will be discharged and the premises should not be reoccupied until they have fully recharged (which could take 24 hours or so).
 
The main problem with wiring as Risteard says is the 'trained' person forgets to turn the keyswitch back on. Easily done with a maintained fitting as the only giveaway is there is no green/red indicator light. An even bigger problem if the lights are designed to be on 24/7 or on a PIR etc so they are switched on at the time of the test.

Seen it happen a few times. On one occasion it caused problems when the keyswitch had been left off by accident. The battery discharged, had a power cut and no emergency lighting.

IMO whatever the regs say, both ways of doing it have their merits/flaws and sometimes one might be more suitable than the other.
 
IMO whatever the regs say, both ways of doing it have their merits/flaws and sometimes one might be more suitable than the other.

I really can't agree. An emergency lighting installation must comply with BS 5266 as well as BS 7671. It would be pretty foolish to claim that non-compliance with the emergency lighting Code of Practice was reasonable.
 
To be fair if the charge indicator ceases to illuminate (but illuminates when the supply is restored) then it would seem reasonable to assume that an emergency luminaire had been running off the battery during test.

As for lux levels etc. these do not need to be determined during the monthly test etc. If you wanted to determine them at another time this could easily be achieved by isolating all of the lighting in the area when it is dark (and when the building is not in use of course). That doesn't mean that the test switch isn't suitable for ensuring the emergency luminaires are operating on failure of the supply.

It should also be remembered if running a full duration test that the batteries will be discharged and the premises should not be reoccupied until they have fully recharged (which could take 24 hours or so).
Sorry, didn't realise that the sole purpose of the test was to check the indicator lights.
I would have thought a test to check that the em lights function as designed would be a good idea.
I guess it all depends on the reason why the em lights have been installed?
If they have been installed just to pander to some safety code, then checking the indicator lamps function may be enough.
If however they have been installed to provide adequate lighting in the event of a failure of the normal lighting, then a test to ensure that they do provide the adequate lighting required would to my mind be sensible.
 
Sorry, didn't realise that the sole purpose of the test was to check the indicator lights.
I would have thought a test to check that the em lights function as designed would be a good idea.

The point is if they illuminate (if non-maintained) or remain illuminated (if maintained) after killing the supply (as verified with the charge indicator) then you do know that they are operating from the battery. The monthly test is only a simple walk-round to verify that the lamps are illuminating and that they have returned to charging mode afterwards. So the keyswitch is ideal for it.
 

Reply to Am I being harsh? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top