Determine the maximum permitted value of voltage drop for each of the following circuits.

a) A 230V lighting circuit supplied directly from a public low-voltage distribution system. (1 mark)
b) A 400V three-phase motor circuit supplied from a factory transformer. (1 mark)
c) A 230V immersion heater circuit in a domestic installation.

a) 3% 6.9v
b)
c) 5% 11.5v

i dont know the answer to b, i am assuming its 5%, but why the difference between a and c? i would have thought all 230v circuits would be 3%?

there is not a lot of info on vd in gn3, i am going to have a look through amberleafs sticky

Have a look at Appendix 12 in BS 7671 it covers VD only.
 
Hi

for single phase 3% for lighting 6.9v
5% for power circuits and distribution 11.5v
and for the answer to b) its 20V which is 5% of 400v

no sorry i am wrong its not 20V as its there own supply not sure

I'm guessing it's 5% per phase so it's 11.5V at each phase where the equipment is installed, not measured between phases.
But I'm guessing.
Sorry it's 8% from a private supply source (This is a new one for me) so I am guessing it is 8% per phase = 18.4 V
But it's just a guess so hopefully I'll be put right by someone.
 
Last edited:
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.
 
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.

Spot on, the percentage is actually of 400 Volts ie. 32 Volts
 
the loop length for circuit 1 is 50 m long the ze is is 0.11 ohms

determine showing all calculations the r1 + r2 and the expected zs

7.41 x 50/1000 = 0.37 12.10 x 50/1000 = 0.60

zs = ze + (r1 = r2)

0.11 + (0.37 + 0.60) = 1.08

have i done this correctly?
 
Last edited by a moderator:
the loop length for circuit 1 is 50 m long the ze is is 0.11 ohms

determine showing all calculations the r1 + r2 and the expected zs

7.41 x 50/1000 = 0.37 12.10 x 50/1000 = 0.60

zs = ze = (r1 = r2)

0.11 + (0.37 + 0.60) = 1.08

have i done this correctly?

I can't confirm the mOhm values but the maths is correct.

You MUST use (R1+R2) when doing these calculations and remember that r1, rn and r2 are reserved for ring continuity figures, this exam is very big on correct terminology.
 
Have a look at the question as it tells you the voltage is 400v three phase.

So its 8% of the 400v if the low voltage installation is supplied from a private low voltage supply.

Hope this helps.

just ordered a set of regs from fleabay so they should be with me in the next couple of days - the only problem i found with the regs in the past was navigating them, i always favoured the on site guide for obvious reasons
 

Reply to An Awful Feeling This in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone, Sorry, I won't take much of your time. To cut a long story short, I am newly qualified and have domestic installation/commercial...
Replies
0
Views
498
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
899
Hello! I am looking for a company to allow me to get more electrical experience. I am mid 30’s, ex military officer and currently training on the...
Replies
2
Views
1K
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
765
I have read all I can find about radio 4 and tele switching, but can't find if this changes when our clocks change. It all started when I decided...
Replies
3
Views
336

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock