Your answer is right it does not comply.
I would have used the equation (mV/A/m)x Ib xL /1000 4.4 X 45 X 80 /1000 = 15.84 V
I see you have used (m ohms/m) x 2 x1.2 which gives you the the mV/A/m anyway.
On the question paper it will give you a table of mV/A/m for the different sizes of cables they won't expect you to remember them its the equation that you need to remember.
Good luck with the exam!!!
I would have used the equation (mV/A/m)x Ib xL /1000 4.4 X 45 X 80 /1000 = 15.84 V
I see you have used (m ohms/m) x 2 x1.2 which gives you the the mV/A/m anyway.
On the question paper it will give you a table of mV/A/m for the different sizes of cables they won't expect you to remember them its the equation that you need to remember.