Search the forum,

Discuss Bathroom refit, do I need a RCD? in the UK Electrical Forum area at ElectriciansForums.net

And a difficult question to answer, but I won’t hold you to it, if nothing changes, is the Flat likely to fail a EICR on the Consumer Units alone I.e. age and lack of ECB, assuming everything else in the flat is ok?
Do you know if there is supplementary bonding in the bathroom? If there isn't it would be much easier to change the CU than to add it.
Assuming it does have the supplementary bonding, and noting it is a a top floor so no sockets are likely to be used outside, it wouldn't have automatic C2's fail for lack of RCD protection according to BPG4. This assumes the installation tests as fault-free in every other regard.

No one should be entertaining a rental property without RCD protection these days though, it's just common sense that you want tenants to have a level of safety that is now commonplace among dwellings.
 
Hi Tim, thanks for your answer.
I accept that RCDs should be fitted for rentals and that is something to consider.
Re the sup. bonding. The pipes are all plastic (save the toilet) so there is nothing to bond. There is a bit more detail on that in my first post.
So given the plastic pipes and if the Flat passes all tests, there is no obvious reason why the current CUs should cause a fail assuming they are in good order?
How would a tester go about checking the plastic pipes?
 
I'd be very wary of renting it out with no RCD protection anywhere.
Yes, understood. I have been told I need an EICR by the management company. I’m starting to think that they have this wrong as I’m the owner and it’s not going to be rented in the near future anyway.
As it’s just me, I’m happy without any RCDs especially due to the cost ( I’m guessing hundreds of £s) but I’m worried that when I get it inspected it will fail. Now I’m questioning if I need to get it inspected at all?
 
Another thought.

In a building such as yours, each flat is its own fire compartment. This means that surfaces like ceilings are specified and installed as fire barriers.
Turning a fire barrier into something resembling swiss cheese to fit a few downlights need special consideration.

You must, must fit fire-rated downlights so that, should a fire start in your fire-compartment, that it cannot spread quickly, through your downlight holes and into the roof of the building.
 
Another thought.

In a building such as yours, each flat is its own fire compartment. This means that surfaces like ceilings are specified and installed as fire barriers.
Turning a fire barrier into something resembling swiss cheese to fit a few downlights need special consideration.

You must, must fit fire-rated downlights so that, should a fire start in your fire-compartment, that it cannot spread quickly, through your downlight holes and into the roof of the building.
A good thought, the downlights I was thinking of are 60 minutes rated (which exceeds that of the current single layer of 12mm plasterboard) IP65 rated and Insulation Contact rated. The loft space is compartmentalised from the other flats. It is a 2 story building with 6 flats.
 
A good thought, the downlights I was thinking of are 60 minutes rated (which exceeds that of the current single layer of 12mm plasterboard) IP65 rated and Insulation Contact rated. The loft space is compartmentalised from the other flats. It is a 2 story building with 6 flats.
A single layer of standard Gypsum plasterboard has no specific fire-resistance.
Your ceiling is probably one of the Fireline products - these are 15mm and covered with pink, not brown paper.
 
A single layer of standard Gypsum plasterboard has no specific fire-resistance.
Your ceiling is probably one of the Fireline products - these are 15mm and covered with pink, not brown paper.
I hope you’re right. It looks like standard board though and I’ve been around a lot of plaster board. Anyway, I probably won’t fit downlights now. Can’t afford for it to fail the EICR tests at the moment.
 
Do you know if there is supplementary bonding in the bathroom? If there isn't it would be much easier to change the CU than to add it.
Assuming it does have the supplementary bonding, and noting it is a a top floor so no sockets are likely to be used outside, it wouldn't have automatic C2's fail for lack of RCD protection according to BPG4. This assumes the installation tests as fault-free in every other regard.

No one should be entertaining a rental property without RCD protection these days though, it's just common sense that you want tenants to have a level of safety that is now commonplace among dwellings.
Hi again Tim, when I get it tested, how does the tester assess the supplementary bonding? If it is by inspection should I remove the bath panel so that they can see the pipes?
 
Yes, understood. I have been told I need an EICR by the management company. I’m starting to think that they have this wrong as I’m the owner and it’s not going to be rented in the near future anyway.
As it’s just me, I’m happy without any RCDs especially due to the cost ( I’m guessing hundreds of £s) but I’m worried that when I get it inspected it will fail. Now I’m questioning if I need to get it inspected at all?
So I have now read that a domestic dwelling should have a EICR every 10 years and if rented every 5 years
 

Reply to Bathroom refit, do I need a RCD? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My EICR test guy says I need to change my bathroom ceiling light to an IP65 rated. Research says I need an IP44. The lamp is about 2.45m above the...
Replies
11
Views
2K
My extractor fan has given up the ghost this week and I was hoping to replace it myself, however I cannot do a like for like swap as the current...
Replies
1
Views
1K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi, I live in a property built in 1911. It has had asbestos artex applied to every ceiling in the house. I am currently creating a new...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock