So if not non-combustible… C3 every day.
I had an email conversation with a representative of the JPEL-64 committee over this some time ago. This was in the context that the (then) new regulation had suddenly made a very large number of (in some cases) very newly installed CUs somehow "dangerous". Bear in mind that a lot of organisations won't allow any C3s to be left - they insist on having a "clean" EICR as that's the only way to avoid "but there was a known and documented risk and you did nothing about it, and no it's caused me loss/injury/whatever" type claims. Even before the introduction of mandatory EICRs, I would get periodic ones for my rental properties - and I would not leave any C3 un-fixed for just that reason (yes, there are some people who would look for any opportunity to exploit it).
Anyway, the response I got was that it was expected that it would be C3 if (for example) the CU was under wooden stairs or in a fire escape route, and not mentioned otherwise. But I couldn't get that as anything more than "a personal opinion" even though it was clear that it was in fact guidance from the committee.

Don't forget that most of the plastic cases previously used will have been various self extinguishing and/or fire retardant plastics. So in the absence of a sustained source of heat, they would not continue burning. As it is, if you have the same sustained source of heat, a steel case can a) allow flames to escape (the standard for CUs doesn't mandate it present a fire barrier) and/or b) set fire to the the wood it's screwed to when it gets hot enough. Of course, if we hadn't mandated such a mass meter change program (which now doesn't actually carry a positive cost-benefit after various supposed benefits failed to be possible), and been forced to use so many "poorly trained" fitters, then we'd not have the problem anyway.

Regardless, it's a stain on the reputation of the JPEL-64 committee until they fix this - which could easily be done by changing the regulation to "non-combustible as per <some existing standard>" as that would allow other materials since it would be possible to test to a known specification. As it is, without the "ferrous metals are deemed" note, then steel would not be allowed since that is combustible if you apply enough heat and oxygen (note, the reg doesn't specify what conditions it has to be non-combustible in) - which makes a complete mockery of the reg.
 
Re introducing a fourth test result category would help, by allowing an easy distinction between 'needs improvement' and 'doesn't comply with current regs, but did at time of installation'.
 
I took a look at the report. The summary is satisfactory with no C3. Item 4.18 is N/A, item 4.19 Pass.
Agreed 4.18 No SPD = N/A but surely 4.19 should be N/A too as no sign of an AFDD on the photo of the CU in #1. How can you 'Pass' something that isnt there? and yet omitted the fact that Fusebox RCBO's have been installed in another manufacturers board (see #3).
 
...surely 4.19 should be N/A too as no sign of an AFDD on the photo of the CU in #1.
I was under the impression that 4.19 was a pass with ref to the three RCBOs that had been fitted. i.e RCD(s) provided for additional protection / requirements - includes RCBOs (411.3.3; 415.1).
 
I was under the impression that 4.19 was a pass with ref to the three RCBOs that had been fitted. i.e RCD(s) provided for additional protection / requirements - includes RCBOs (411.3.3; 415.1).
The NICEIC DEICR checklist is
1681924021909.png


But you may be correct with another (eg Napit) checklist
 

Reply to Boiler, programmer etc. via immersion heater circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Wonder if anyone can help out, my experience in heating is minimal. So house I was working in had a circuit for the water heater, which went to a...
Replies
4
Views
388
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
678
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
Replies
43
Views
6K
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
818

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock