hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
u aint just a pretty dude tony are you.... when i was working there today i found half pack of 5A fuses lying on top of cu .
would you say with the fuse keep blowing would destroy the lamps aswell in some way.
 
also, it's common for the fuse to blow when a lamp fails (more so with MCBs). an anti-surge (motor rated) fuse may cure your problem though.
 
bad idea.15A is a tad to high a rating for 1.5mm T/E . even worse if it's wired in 1.0mm. better would be to split the lighting into 2 5A circuits.
 
isnt 1.5mm rated at 18-20A or something tel. too much work involved in splitting the lighting circuit. ive told them to change to energy efficent lighting (led) just weighing up mu options for monday morning
 
10A fuse in the FCU, would be better. even better would be to replace the GU10 halogens with LEDs. ssimmples
 
But remember a fuse is there to protect the circuit from damage so you still have the problem of an oversuze fuse at the origin of the circuit.......theres nothing to stop someone removing the fcu in future and just relying on the fuse at the board which at 15A is too much for 1mm............
 
1mm can take 16A if i remember right, the circuit is 1.5mm t&e. i aint as expierienced as i think i am so keep them comming sparkys.. where you get a 10A fuse tel, never seen one before or have i, naw i i havent hey
 
good point. glenn. methinks I=P/U is looking for a quick fix. not a good idea. could try a 6A or a 10A MCB though , after a 15A fuse in the board.
 
well i think change the lamps is easies option, what about that fuse that allows inrush currents tel, do they exsist that will fit in 1361 fuse carrier. if i changed to 6A or 10A mcb wouldn't that mean the zs would change and maybe not meet the requirements.
 
i=p/u The steady current drawn by a lamp is when it is at its operating temperature which for incandescent lamps is around 2000 deg C the initial current draw at 25deg C can as as much as 5 -10 times the steady current. So switching all switches together gives a massive surge just like a motor starting current.
Put in the largest fuse permissible for the circuit cable and advise customer to switch the switches one at a time
If you uprate the fuse you need to confirm the Zs still meets the 0.4 disconnection time
 
Last edited by a moderator:
was thinking c type breaker too but why 2.5mm for 15A fuse. am i missing something reallly badly here.. do you think would still trip the blow 15A fuse, the type c breaker does sound the pigs ears
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
 
Last edited by a moderator:
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A
yep. got it platty (p) 282...thank you. :crazy:
 
1.5mm T&E ref method C (clipped direct )or buried in masonry has a max current 20A page 228 BS7671 Max Zs 1.70 at 70 deg so 1.7 x 0.8 = 1.36
If Zs is measured at less than 1.36 at furthest point on circuit and cable is installed Ref method C then 15 Fuse should be OK

559.6.1.6 max overcurrent device for normal lighting circuits 16A

Think a GU10 Lamp holder might not come under that regulation
 

Reply to bs 1361 fuse in the Australia area at ElectriciansForums.net

Similar Threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top