Cable buried in a flower bed

Discuss Cable buried in a flower bed in the UK Electrical Forum area at ElectriciansForums.net

Pretty Mouth

-
Esteemed
Arms
Reaction score
2,878
Had a look at a job a few days ago where, should the work go ahead, it would be necessary to run a cable under a flower bed. This is the only option acceptable to the customer unfortunately. The cable will be low voltage, ELV is not an option as the cable will supply power to sockets.

The flower bed is raised by about a foot, is narrow, and lies between a path and a fence. I suspect the concrete holding the fence posts will prevent me burying the cable to a decent depth.

Has anyone got any clever ways of protecting such a cable from damage when the flower beds get dug over?
 
Thanks for the comments guys, it's a great help.

The customer doesn't want the cable clipped to the fence unfortunately. She is quite particular about minimising visible cables. I'll not know until I start digging, but looking at it, I'm not at all confident I'll be able to get deep enough to avoid contact from spades when digging.

On a similar job I was able to run the cable in conduit, then bed a course of bricks of bricks on top. It worked well because there was brickwork immediately below the conduit too (it was a brick built raised bed), so was totally solid. I'm not sure that would work as well in this instance, as much of the run will probably be soil beneath. Perhaps that doesn't matter though.
 
You could get scaffold tube which is 45mm + internal diameter 2 Metre Aluminium Tube - Alloy Scaffolding Tube - https://www.scaffolding-direct.co.uk/alloy-scaffolding-tube-48mm-tube-clamp-key-clamp-tube-or-scaffolding-4.aspx

And then line it on the inside with plastic 32mm pipe FloPlast Solvent Weld Waste Pipe White 32mm x 3m - https://www.NoLinkingToThis/p/floplast-solvent-weld-waste-pipe-white-32mm-x-3m/61967

If you need to make it really long you could join the tubes together with one of these Pressed Sleeve Coupler Scaffolding Fittings - https://www.scaffolding-direct.co.uk/scaffold-clamp-pressed-steel-sleeve-coupler-25-.aspx

For 32 mm pipe connector FloPlast Straight Couplers 32 x 32mm White 5 Pack - https://www.NoLinkingToThis/p/floplast-straight-couplers-32-x-32mm-white-5-pack/38660
 
A lot comes down to budget. There were once cable protection/marker bricks (?Baldwin) available that were perfect for this kind of thing but they don't seem to be as commonly available now, and the ones that turn up on line look expensive.
(And as I found out once, they aren't plumber proof when someone hands over the keys to a mini-digger...)

I'm assuming that galv conduit is too much of a faff to consider? Most manufacturers state it requires no extra anti-corrosion protection when in soil or concrete.
On that basis is galv trunking too expensive and over the top?
 
A lot comes down to budget. There were once cable protection/marker bricks (?Baldwin) available that were perfect for this kind of thing but they don't seem to be as commonly available now, and the ones that turn up on line look expensive.
(And as I found out once, they aren't plumber proof when someone hands over the keys to a mini-digger...)

I'm assuming that galv conduit is too much of a faff to consider? Most manufacturers state it requires no extra anti-corrosion protection when in soil or concrete.
On that basis is galv trunking too expensive and over the top?
I'm surprised that manufacturers are suggesting galv conduit for direct burial in soil. I would've thought it would rust through eventually?
 
I had considered this, perhaps using black pipe with electrical warning tape wrapped around it. Have seen this done a couple of times on farm instalations, and it seemed to work well, it is very tough. Kinda breaks a reg or 2 though doesn't it?

How about flexible ducting wrapped with tape? Still fairly tough and no regs contravened.
 
I'm surprised that manufacturers are suggesting galv conduit for direct burial in soil. I would've thought it would rust through eventually?
I would expect so. You can get stainless but at a price:

 
My first thought was plastic conduit but obv a spade can break through this. Then i thought that cheap ali pipe you can get from DIY shops but then it'd need earthing.

Personally i'd just run it in a piece of metal conduit with a through-box for access and fly lead it on the inside for the earth.
 
Thanks for the comments guys, it's a great help.

The customer doesn't want the cable clipped to the fence unfortunately. She is quite particular about minimising visible cables. I'll not know until I start digging, but looking at it, I'm not at all confident I'll be able to get deep enough to avoid contact from spades when digging.

On a similar job I was able to run the cable in conduit, then bed a course of bricks of bricks on top. It worked well because there was brickwork immediately below the conduit too (it was a brick built raised bed), so was totally solid. I'm not sure that would work as well in this instance, as much of the run will probably be soil beneath. Perhaps that doesn't matter though.
I think any additional mechanical protection you add will help, ideally something that won't easily dislodge if struck by a spade.
 
Thanks again all, this gives me a few ideas to work with.

I attacked a piece of rigid plastic conduit with a spade to see how it fared. It did better than I expected, and took a few good whacks before I was able to break into it.

I suppose a lot will depend on the quality of the conduit and the outside temperature. I agree though, some plastic tubing is remarkably tough.
 
PVC conduit is pretty tough , you really have to give it a good whack with a hammer to crack it

many many years ago we got some pvc conduit from a wholesalers and it was described as unbreakable , naturally i put this to the test and yep even after about 15-20 whacks with a club hammer it wouldn't crack. think it was clipsal brand
 
Armoured burried in soil is good enough, plastic over the top is even better, its dogs dangles if you have black and yellow marker tape to top off. after that tell them you need digger.
 

Reply to Cable buried in a flower bed in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock