Search the forum,

Discuss calculating the de-rating of a cable near a heat source in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Reaction score
13
Im Working on a new build site at the moment, and the kitchen layout has changed to include an island with a hob on it.
Meaning im goin to have to get power to it.

The underfloor heating pipes have been run in already and the floor has been screeded.
Theres about 50mm before you get to the pipes. Pipes will reach 50 degrees max
My questions are;

1. Does anybody know if its against the regs to do this?

2. how can i calculate the de-rating of my cable?
was goin to use 6mm t+e in a conduit
 
Hi NV - I'm thinking Table 4A2 installation method 60, which is ref method B. Then temp derating from Table 4B1. How much load is there on the Island ?
 
Hi NV - I'm thinking Table 4A2 installation method 60, which is ref method B. Then temp derating from Table 4B1. How much load is there on the Island ?
depends on the power rating of the music system playing the desert island discs. :D:D:D.
 

Reply to calculating the de-rating of a cable near a heat source in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock